    Food truck with solar power

    Hi

    Was asked a question - If I fit solar panels and inverter to a food truck how do I ensure that the earthing is correct and that my clients will not end up being " shocked"
    What do I do with regards to the COC .

    The earthing arrangement has me doing some thinking -
    If a Kid comes along in bare feet from the beach and touches the side of the truck at the same time I have a short to "earth" , being the body of the truck, will he then become the path to ground.
    Or do we treat the food truck as an Island

  2. #2
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    Is the solarPV the only power on the food truck or is there a generator and/or a facility to plug into grid power?

    What items is the solar and inverter being used to supply? I'm guessing it's quite a small system purely because of the space available for panels..Is it just for lighting and IT equipment? Is the equipment all ClassII?

    Depending on the answers to the questions above my initial thoughts are to treat it as a UPS.
    _______________________________________________

    _______________________________________________

  3. #3
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,484
    Thanks
    104
    Thanked 141 Times in 134 Posts
    Interesting. What do they do on boats and aeroplanes?

  4. #4
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,648
    Thanks
    3,304
    Thanked 2,676 Times in 2,257 Posts
    Blog Entries
    12
    I suggest treat it as a safety supply system. As long as all exposed metals are at the same potential (i.e. electrically bonded together), and there is no other conductor between ground and the exposed metal to carry a fault current, even if for some reason you do end up with a significant potential difference, the most current you can have is that typical of a static discharge.

    If you have an external (mains) power supply as well as the solar system and inverter, connect it to the installation via a safety supply transformer.

Similar Threads

  1. Solar power panels
    By reggy in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 28-Feb-23, 10:25 PM
  2. solar power inverter issues
    By markthespark in forum Electrical Contracting Industry Forum
    Replies: 4
    Last Post: 04-Aug-16, 09:38 PM
  3. Truck Driver threatens to leave the truck and the keys
    By SSS100 in forum Labour Relations and Legislation Forum
    Replies: 10
    Last Post: 01-Feb-12, 08:17 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •