    ELU turns off after power goes back on

    I can recall some one posting something of this nature some time back, but after load shedding
    this particular earth leakage unit trips. It can be reset straight away and all is well.

    Has anyone experienced this type of thing and what could be causing it.

  2. #2
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,236
    Thanks
    34
    Thanked 304 Times in 258 Posts
    There could be surge arrestor plug tops on the circuit - On switch on there are slight surges been taken to earth which causes the imbalance and the unit trips.
    Switch mode power supplies, like found in PC''s , also have a habit of doing that.

  3. #3
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,484
    Thanks
    104
    Thanked 141 Times in 134 Posts
    Quote Originally Posted by ELECT 1 View Post
    I can recall some one posting something of this nature some time back, but after load shedding
    this particular earth leakage unit trips. It can be reset straight away and all is well.

    Has anyone experienced this type of thing and what could be causing it.
    Was called out yesterday for the same thing.

    It was one of those old 20 mA sensitivity units.

    We created our own blackouts by turning the main breaker off and then on again and each time, the unit would trip.

    Replaced with a new CBI 30 mA ELR and problem solved.


    Cheers & peace out ... Derek

  4. Thanks given for this post:

    ELECT 1 (12-Mar-20)

  5. #4
    Full Member
    Join Date
    Dec 2013
    Location
    Western Cape
    Posts
    78
    Thanks
    17
    Thanked 5 Times in 3 Posts
    Yip, i also just replaced it.

  6. #5
    Full Member
    Join Date
    Aug 2018
    Location
    Capetown
    Posts
    42
    Thanks
    0
    Thanked 1 Time in 1 Post
    I also found that surge arrester plugtops(0.1 mega ohms),transformers in gate motors (0.5 mega ohms) and the transformer for the alarm(0.5 mega ohms) would just wait for something to trigger them.

  7. #6
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    The question is did you fix the problem or just prolong it... get a current clamp meter which can test mA ...you will be able to determine if it was at the threshold which caused it to trip already or if it was just a faulty e/l unit.

    Just remember to put the insulation resistance on 250 V so that you dont pop the MOVs in the plug tops.
    Comments are based on opinion...not always facts....that's why people use an alias.

  8. #7
    Full Member
    Join Date
    Aug 2018
    Location
    Capetown
    Posts
    42
    Thanks
    0
    Thanked 1 Time in 1 Post
    I found that with the transformers and surge arrester plugtop the earth leakage sensitivity was less than 10ma and with them isolated the sensitivity was between 25ma and 30ma. So I wrote it in my report and suggested the replacement of transformers and taking of plugtop to prevent nuisance tripping.

Similar Threads

  1. Could it be true if Nigel February turns out to be a murderer?
    By AnnRichter in forum General Chat Forum
    Replies: 12
    Last Post: 23-Mar-17, 07:32 PM
  2. [Question] Windows 10 Defender - Turns itself back on
    By irneb in forum Technology Forum
    Replies: 9
    Last Post: 09-Mar-16, 11:32 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •