    Electric shock during loadshedding

    We recently had an incident where my wife got quite a shock after touching the gutter down-pipe.
    This happened while we were in load-shedding ??
    The only things that we had running were the alarm system and the electric fence, my assumption is that it had to have something to do with the electric fence to cause such a shock, but can't see any contact point to the roof / guttering to cause this.
    It is clear that the gutters need to be bonded, but any ideas how to isolate the cause of the charge?

  2. #2
    Silver Member
    Join Date
    Jul 2008
    Location
    Germiston, South Africa
    Posts
    397
    Thanks
    24
    Thanked 47 Times in 43 Posts
    Quote Originally Posted by Ash003 View Post
    We recently had an incident where my wife got quite a shock after touching the gutter down-pipe.
    This happened while we were in load-shedding ??
    The only things that we had running were the alarm system and the electric fence, my assumption is that it had to have something to do with the electric fence to cause such a shock, but can't see any contact point to the roof / guttering to cause this.
    It is clear that the gutters need to be bonded, but any ideas how to isolate the cause of the charge?
    The earthing from the electric fence has to be a minimum distance from the earthing of the house which would also include the bonding of the gutters.
    It's possible that the earthing is closer than allowed and the earth's are interfering with each other.


    Sent from my SM-A705FN using Tapatalk
    To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

  3. #3
    New Member
    Join Date
    Feb 2020
    Location
    Gauteng
    Posts
    2
    Thanks
    0
    Thanked 0 Times in 0 Posts
    thanks Leecatt, the gutters need to be bonded no question, the fence is earthed on the other side of the garden nearly 24 m away from the DB

Similar Threads

  1. Nuisance E/L tripping only @ loadshedding
    By joshthejew in forum Electrical Contracting Industry Forum
    Replies: 6
    Last Post: 16-Dec-20, 05:46 AM
  2. An idea for ending loadshedding
    By Derlyn in forum Electrical Contracting Industry Forum
    Replies: 15
    Last Post: 18-Feb-20, 08:13 AM
  3. [Article] US Federal Reserve Shock 2012 Move Dooms America
    By Frankincense in forum General Business Forum
    Replies: 33
    Last Post: 16-Feb-10, 10:27 AM
  4. Interest rate shock
    By QUINN in forum General Business Forum
    Replies: 5
    Last Post: 27-Jun-09, 12:30 PM
  5. Loadshedding early warning
    By JTech in forum Electrical Load Shedding Forum
    Replies: 9
    Last Post: 22-Apr-08, 03:31 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •