    load shedding fix

    I have 3 inverters installed in parallel which supplies a house with 2 outbuilding....3 geysers ...entertainment area ...pool pumps etc.

    All connected to a 60 amp single phase supply.

    Here's the challenge ...geysers ...pool pumps and other non essential supplies... they drain the batteries too quickly.

    I need a solution to this problem... i could run control wires to each device and fit a contactor or relay ...the problem is the distance and access to the various locations...something like the old ripple relay system the municipality used back in the day.

    The other thought was to fit wireless unit ...like a sonoff ...a receiver...wifi unit or even bluetooth to control the device when the power turns off.

    It sounds simple however ...each item is fed via a sub DB with a pre paid meter which has other stuff like fridges etc.

    What i am looking for a simple wireless solution to control these devices without having to separate them from the sub DB they are connected... there was an attempt to separate them via the main DB ...however this no longer works because the sub DBs now have prepaid meters.

    Power goes off...a signal is sent to all the devices to shut down and when the power is back on... a delay staggering the power on to each device ...preventing a heavy load on the system.
    Comments are based on opinion...not always facts....that's why people use an alias.

  2. #2
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,246
    Thanks
    34
    Thanked 304 Times in 258 Posts
    Hi Ians

    Can you adjust the frequency output of the inverter ? if so then you could increase/decrease the frequency with mains fail and use a frequency monitor to drop a relay out
    I know ACDC do a monitor at list price of R 297.00 - I am sure others do as well

    https://www.acdc.co.za/pages/product...l?FR1%20230VAC

  3. #3
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    GCE thanks for the suggestion.

    I have spoken to a few people and there were many suggestions ...but the one i am thinking of doing is the solid state relay option ...will go into more detail when i get a chance..everyone is waiting for dinner.
    Comments are based on opinion...not always facts....that's why people use an alias.

  4. #4
    Diamond Member
    Join Date
    Mar 2010
    Location
    Cape Town
    Posts
    6,329
    Thanks
    426
    Thanked 978 Times in 795 Posts
    Why don't you faff with RaspBerry PI or ESP2866 IOT devices. You can build a IOT WiFi network with GSM backup fairly easily.

  5. #5
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    I was thinking wireless ...but i think it might be better to run a low voltage control wire and use solid state relays to switch the devices off.

    This also brings a few challenges... solid state relays are not designed for long on/off periods more short fast switching... then we have the heating to take into consideration.

    My thoughts are to use a high current rating SSR to switch the devices which will draw around 10 - 15 amps ...wired via the timer for the pool pump and the thermostat on the geysers.
    Comments are based on opinion...not always facts....that's why people use an alias.

  6. #6
    Full Member
    Join Date
    Nov 2019
    Location
    Alberton
    Posts
    67
    Thanks
    2
    Thanked 4 Times in 4 Posts
    Hi Ians,
    The sonoff switches are great and cheap thats if you have wifi for them, can be a bit of a challenge if distance is too far.
    Sonoff could control pool pump and geysers and be scheduled to come on during the day only with good PV and set the timers so that pool and geyser does not come on say after 17H00 to save battery power.
    I have mine wired in such a way that the inverter powers the sonoff, in other words only when I am off-grid do the sonoffs function because they then control my loads. When my grid power is back on the sonoffs does not have power so they then have no effect over my loads and everything work as normal.

Similar Threads

  1. COC and load shedding
    By ELECT 1 in forum Electrical Load Shedding Forum
    Replies: 11
    Last Post: 13-Jun-15, 08:24 PM
  2. Load shedding
    By ians in forum Electrical Contracting Industry Forum
    Replies: 22
    Last Post: 11-Mar-14, 01:45 PM
  3. Who does not believe load shedding is still with us?
    By Marq in forum General Chat Forum
    Replies: 16
    Last Post: 10-Sep-09, 07:55 AM
  4. no load shedding?
    By murdock in forum Electrical Load Shedding Forum
    Replies: 0
    Last Post: 24-Jul-08, 08:13 PM
  5. load shedding
    By murdock in forum Electrical Contracting Industry Forum
    Replies: 7
    Last Post: 27-May-08, 11:40 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •