Thread: SANS 6.14.1.2

  1. #1
    Full Member
    Join Date
    Oct 2012
    Location
    Durban
    Posts
    66
    Thanks
    0
    Thanked 5 Times in 4 Posts

    SANS 6.14.1.2

    Hi. I would like to hear anyone's understanding on SANS 6.14.1.2. It mentions that a four pole disconnecting device to be used in a multi phase circuit supplying single phase lights. It states that all phase conductors and neutral need to be isolated but the confusing part is that it is to perform maintenance work without switching off all the lights but with all phase conductors and neutral isolated all the lights will be off.

  2. #2
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    6.14.1.2 Each identified group of single-phase luminaires supplied from a
    multiphase supply that also feeds other luminaires, shall be controlled by a
    local multiphase disconnecting device.


    If you have a single phase lights that are fed from a 3-phase circuit then you need to have an isolator that disconnects the 3-phases, not just the phase those lights are on.

    Here's another recent discussion about the same reg; https://www.theforumsa.co.za/forums/...eaking-Neutral
    _______________________________________________

    _______________________________________________

  3. #3
    Full Member
    Join Date
    Oct 2012
    Location
    Durban
    Posts
    66
    Thanks
    0
    Thanked 5 Times in 4 Posts
    Quote Originally Posted by AndyD View Post
    6.14.1.2 Each identified group of single-phase luminaires supplied from a
    multiphase supply that also feeds other luminaires, shall be controlled by a
    local multiphase disconnecting device.


    If you have a single phase lights that are fed from a 3-phase circuit then you need to have an isolator that disconnects the 3-phases, not just the phase those lights are on.

    Here's another recent discussion about the same reg; https://www.theforumsa.co.za/forums/...eaking-Neutral
    Thanks Andy.
    I get that part. Its the neutral that I am concerned about. It would appear that to feed a circuit of single phase lights from a 3 phase supply I will need to install 4 pole circuit breakers as opposed to 3 pole circuit breakers. I can think of numerous examples where there are only 3 pole C/B's. This is an industrial application and the lights are fed directly from a Small Power and Lighting DB with no light switch.

Similar Threads

  1. New sockets - sans 164-2
    By skatingsparks in forum Electrical Contracting Industry Forum
    Replies: 30
    Last Post: 26-Apr-19, 09:39 PM
  2. [Article] SANS 164-2
    By SeanM in forum Electrical Contracting Industry Forum
    Replies: 18
    Last Post: 03-Jul-18, 09:53 AM
  3. [Question] SANS 10400 XA
    By Les Abbott in forum Energy and Resource Conservation Forum
    Replies: 0
    Last Post: 01-Jun-17, 01:20 PM
  4. sans 724 and sans 984
    By murdock in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 31-Jul-10, 04:35 PM
  5. SANS codes.
    By I Robot in forum Electrical Contracting Industry Forum
    Replies: 48
    Last Post: 09-Apr-10, 07:52 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •