    DB Board Breaking Neutral

    Hi All,

    I keep hearing that we now supposed to break the neutral on ALL circuits in a DB … i.e. install double pole circuit breakers as a general rule.

    I don't see any reference in SANS 10142 that confirms this … (apart from fixed appliances etc.)

    Can anybody confirm this ? And if not specifically mentioned in SANS … what is the general standard for lighting and plug circuits in commercial buildings ?

    Thanks

  2. #2
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,236
    Thanks
    34
    Thanked 304 Times in 258 Posts
    Hi
    Plugs and lights circuits are generally 20 amp and 16 Amp on any site
    Besides the normal fixed appliance and generator circuits there is a requirement under lighting.

    Breaking of the neutrals can happen and be compulsory on 3 phase lighting circuits - I have heard the interpretation previously that all light circuits must be double pole but disagree and don't believe that the code is worded as such.Besides the fact that the note just seems to throw more confusion.
    I read the regulation as to stop the possibility of having a floating neutral when working on a 3 phase lighting circuit.

    6.14.1.2 Each identified group of single-phase luminaires supplied from a
    multiphase supply that also feeds other luminaires, shall be controlled by a
    local multiphase disconnecting device.
    NOTE The disconnecting device should disconnect all live conductors that feed the
    group of luminaires, including the neutral, in order that maintenance work can be
    carried out without switching off all the lights

  3. #3
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,479
    Thanks
    134
    Thanked 695 Times in 593 Posts
    Blog Entries
    1
    Besides SANS, in my book it is good practice to have double pole disconnect devices in the DB board for single phase circuits.
    Effectively single phase DB boards are ultimately fed from a 3 phase supply, and with the prevalence of cable theft, where thieves are targeting only the removal of the Neutral because it is safe to do so, cause the Neutral in loads down the line to cause dangerous voltages being back fed from 3 phase loads, and simply disconnecting the Live, does not protect the single phase DB load unless the Neutral is also disconnected as well as part of the protection.

    Had this problem last week, with the Red phase destroying many equipment that was connected on this phase due to a supply fault.
    I was not able to get the actual issue from the municipality, but took them 2 days to fix the problem. Even had TV catching fire due to the fault, and a light switch catching fire which was supplying a number of fluorescent lights. Interestingly the earth leakages did not trip, only breakers due to the overloads once the equipment failed.
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

  4. #4
    Junior Member
    Join Date
    Oct 2018
    Location
    Gauteng
    Posts
    19
    Thanks
    2
    Thanked 2 Times in 2 Posts
    Thanks Guys. I find SANS a difficult read.

    Elsewhere it says "NOTE 3 Unless specified elsewhere in this part of SANS 10142 for a particular application, the protective device need not disconnect the neutral conductor". This is not very helpful as it is very difficult to find where it does specify to break the neutral leaving a lot to our own interpretation … which should not be the case.

    then "6.9.2.2 In the case of a single-phase circuit, the disconnecting device shall disconnect live and neutral." Now what does this refer to ? If it refers to the DB main disconnecting device then fair enough. But it says circuit … so I may interpret a normal 16A lighting circuit as a "circuit" then then this "circuit" must have a double pole disconnecting device?

  5. #5
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    My advice...be very careful disconnecting neutrals...especially on 3 phase systems... i have seen a few which didnt end well for the sparky.

    Its like thinking you are too clever and dont switch off the light circuit... but instead just turn off the switch...thinking all is good... the light in the room next door is switched on and it bites you.

    I have also seen a few nasty outcomes with sparkies working on single phase socket outlets in office blocks which are fed via a 3 phase system... they get all the neutrals mixed up and dont label the wires... it happened to me a long long time ago... I blew all the computers in an office next door to where i was working on the same floor.
    Comments are based on opinion...not always facts....that's why people use an alias.

  6. #6
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,648
    Thanks
    3,304
    Thanked 2,676 Times in 2,257 Posts
    Blog Entries
    12
    Quote Originally Posted by RobertZA View Post
    then "6.9.2.2 In the case of a single-phase circuit, the disconnecting device shall disconnect live and neutral." Now what does this refer to ? If it refers to the DB main disconnecting device then fair enough. But it says circuit … so I may interpret a normal 16A lighting circuit as a "circuit" then then this "circuit" must have a double pole disconnecting device?
    I suggest the full reading of 6.9.2 gives us the context.

    6.9.2 Disconnection of neutral conductors

    6.9.2.1 A neutral conductor shall not have a single-pole disconnecting device.

    6.9.2.2 In the case of a single-phase circuit, the disconnecting device shall disconnect live and neutral. In the case of a multiphase circuit, the disconnecting device shall disconnect all the phase conductors but need not disconnect the neutral conductor in an installation connected to a supply system in which the neutral conductor is earthed direct (see the TN system in annex J).

    6.9.2.3 A disconnecting device used in a supply system in which there is no direct connection between earth and any live conductor shall disconnect all the live conductors (see the TT and IT systems in annex J).

    NOTE In a safety supply, none of the conductors are connected to earth, so any disconnecting device in such a circuit has to disconnect all the conductors.

    There is no instruction here that every circuit requires a disconnecting device. The purpose is to instruct which conductors any disconnecting device must disconnect given the situation in which they have been placed.

    An observation on disconnecting the neutral in 3 phase circuits - the neutral should* be the last conductor to break and the first conductor to make. If this isn't written into SANS 10124-1 somewhere already, I suggest it should be.

    *Note that "should" becomes "must" per the requirements of some power supply authorities for cross-over switches in installations with alternative supplies.
    Last edited by Dave A; 25-Nov-19 at 06:48 AM.

  7. #7
    Full Member
    Join Date
    Nov 2019
    Location
    Alberton
    Posts
    67
    Thanks
    2
    Thanked 4 Times in 4 Posts
    As per my understanding of SANS the disconnecting device is aimed at a isolator.
    Easy examples is, if you fit a isolator for a single phase geyser circuit it must break live and neutral.
    If you fit a isolator for a three phase air-con unit, it is allowed to break only phase conductors and does not need to break neutral. But you may break the neutral if you prefer.
    Does this sound correct?

Similar Threads

  1. BREAKING NEWS: SereniGy Is Now Pre-Launching In SOUTH AFRICA!
    By SGTeamFreedom in forum MLM Industry Forum
    Replies: 2
    Last Post: 23-Apr-12, 07:45 PM
  2. Is Twitter breaking down?
    By Dave A in forum Technology Forum
    Replies: 9
    Last Post: 18-Aug-09, 04:41 PM
  3. Standard Bank Declines for Second Day After Breaking Credit Law
    By QUINN in forum General Business Forum
    Replies: 6
    Last Post: 01-Jul-09, 07:20 PM
  4. Breaking News
    By SilverNodashi in forum General Chat Forum
    Replies: 0