Results 1 to 6 of 6

Thread: When does a Geyser become a Boiler

Hybrid View

Previous Post Previous Post   Next Post Next Post
  1. #1
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,248
    Thanks
    34
    Thanked 304 Times in 258 Posts

    When does a Geyser become a Boiler

    Hi

    Had an interesting question that has me thinking, trying to decide which way is correct.

    On a hostel type environment they have installed a central hot water system with a +/- 500L tank with 3 phase elements in it.
    The consultants are calling it a boiler and saying that it does not need to be on earth leakage unit.
    If they call it a Boiler it may not need an earth leakage at 30mA but it will need a Adit relay.

    The question I am asking is , when does a Geyser become a Boiler according to SANS 10142-1
    Anybody come across the dilemma ?

  2. #2
    New Member MrZakeQina's Avatar
    Join Date
    Jul 2017
    Location
    Pretoria
    Posts
    7
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Quote Originally Posted by GCE View Post
    Hi

    Had an interesting question that has me thinking, trying to decide which way is correct.

    On a hostel type environment they have installed a central hot water system with a +/- 500L tank with 3 phase elements in it.
    The consultants are calling it a boiler and saying that it does not need to be on earth leakage unit.
    If they call it a Boiler it may not need an earth leakage at 30mA but it will need a Adit relay.

    The question I am asking is , when does a Geyser become a Boiler according to SANS 10142-1
    Anybody come across the dilemma ?
    What's an Adit relay first of all? This is interesting indeed

    Sent from my SM-A305F using Tapatalk

  3. #3
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,660
    Thanks
    3,307
    Thanked 2,676 Times in 2,258 Posts
    Blog Entries
    12


    6.16.2 Water heaters
    NOTE Water heaters include geysers, instantaneous water heaters including units
    for boiling water, heat pumps, solar systems, induction water heaters and the like (see
    also 6.16.1). electrode water heaters, steam generators and boilers are not included
    (refer to 6.16.7)

    From an engineering perspective, the objective of a boiler is to bring the liquid to boiling point...
    A geyser surely is supposed to stop heating well short of boiling point.

    BTW - there's a typo. It should be Electrode (capital E) as it is the first word in the sentence.

  4. #4
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    Quote Originally Posted by Dave A View Post


    6.16.2 Water heaters
    NOTE Water heaters include geysers, instantaneous water heaters including units
    for boiling water, heat pumps, solar systems, induction water heaters and the like (see
    also 6.16.1). electrode water heaters, steam generators and boilers are not included
    (refer to 6.16.7)

    From an engineering perspective, the objective of a boiler is to bring the liquid to boiling point...
    A geyser surely is supposed to stop heating well short of boiling point.

    BTW - there's a typo. It should be Electrode (capital E) as it is the first word in the sentence.
    you must luv reading my posts

  5. #5
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,660
    Thanks
    3,307
    Thanked 2,676 Times in 2,258 Posts
    Blog Entries
    12
    Quote Originally Posted by ians View Post
    you must luv reading my posts
    You're not SANAS

  6. #6
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,248
    Thanks
    34
    Thanked 304 Times in 258 Posts
    Been meaning to come back and post the findings on the original question I posed

    According to the regulations - "Pressure Equipment Regulations of 15 July 2009 " The description pasted below is excluded from the pressure regulation .

    2(3h) fixed electrical hot-water storage container of water capacity
    from 15 litres to 450 litres operating at a maximum pressure of
    600 kPa manufactured to the requirements of SANS 151, which
    shall be installed in accordance with the requirements of SANS
    10254


    If your consultant decides that his so called boiler falls outside of the above scope and therefore does not need earth leakage unit then he will need to comply to the balance of the Pressure regulations and have the unit registered with the DOL and have the unit pressure tested and inspected on a regular basis , every 36 months. The unit will still need to comply with SANS 10142-1 and have a Earth leakage relay at 10% of rated current.

    Would think it is more cost effective in the short and long run to call it a geyser and be finished with it.

  7. Thanks given for this post:

    Dave A (19-Dec-19)

Similar Threads

  1. Geyser trips when hot
    By joshthejew in forum Electrical Contracting Industry Forum
    Replies: 23
    Last Post: 05-Aug-21, 02:52 PM
  2. Geyser not heating
    By Bonga Mkhize in forum General Chat Forum
    Replies: 4
    Last Post: 23-Oct-17, 11:01 PM
  3. Solar Geyser COC
    By julianzimzeni in forum General Regulatory Compliance Forum
    Replies: 10
    Last Post: 10-Feb-17, 11:52 AM
  4. [Question] Switching off geyser
    By IanF in forum Electrical Load Shedding Forum
    Replies: 7
    Last Post: 16-Sep-16, 11:12 AM
  5. [Question] Hi Plz help - how do I turn off my Geyser?
    By Poor Student in forum Electrical Contracting Industry Forum
    Replies: 6
    Last Post: 10-Dec-14, 02:26 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •