Results 1 to 3 of 3

Thread: Plug circuits on breaker?

Hybrid View

Previous Post Previous Post   Next Post Next Post
  1. #1
    Full Member
    Join Date
    Aug 2019
    Location
    Mossel Bay
    Posts
    28
    Thanks
    4
    Thanked 1 Time in 1 Post

    Plug circuits on breaker?

    Good day. I read a few threads back but can't find a related one.

    How many plug circuits may be connected to a 20A breaker?. In other words, may you have two 2.5mm wires connected to the bottom of a breaker that feeds plugs? What does regulation say. Thanks in advance.

  2. #2
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,260
    Thanks
    34
    Thanked 305 Times in 259 Posts
    Hi

    On 20 Amp and 2,5sqmm I would say max 3 - You still need to watch that you circuit will not exceed the 5Kw load state somewhere in the code and there is also a restriction on neutrals and earths .
    Pasted the 2 relevant regs below

    6.1.5 A maximum of three conductors may be connected to any one
    terminal provided that the terminal has the correct rating.

    6.6.1.11 If a conductor of cross-sectional area exceeding 4 mm2 is used, it
    shall be so installed to allow any one neutral conductor to be disconnected
    without disturbing the connection of any other neutral conductor

  3. #3
    Full Member
    Join Date
    Aug 2019
    Location
    Mossel Bay
    Posts
    28
    Thanks
    4
    Thanked 1 Time in 1 Post
    Thanks!

Similar Threads

  1. 5A Unswitched Circuits
    By Jaboel in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 05-Aug-21, 04:28 PM
  2. Settable C/Breaker
    By GCE in forum Electrical Contracting Industry Forum
    Replies: 9
    Last Post: 18-Nov-18, 04:16 PM
  3. Socket circuits and SANS 10142
    By dsmossbw in forum Electrical Contracting Industry Forum
    Replies: 9
    Last Post: 06-Mar-18, 10:49 PM
  4. Dedicated plug circuits, what is allowed to be supplied by a non earth leakage protected socket?
    By hartdev@hotmail.com in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 19-May-17, 06:52 AM
  5. Underfloor heating circuits
    By kosmonooit in forum Electrical Contracting Industry Forum
    Replies: 11
    Last Post: 26-Oct-16, 02:52 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •