    Geyser and plug on mixed circuit

    Any one out can assist me with this query Sans 10142 - 1 does not say thats not allowed so would presume that it legal.

  2. #2
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,236
    Thanks
    34
    Thanked 304 Times in 258 Posts
    Hi

    I would say a geyser is not allowed on a mixed circuit and back the statement up with 6.16.2.2 pasted below

    6.16.2 Water heaters
    NOTE Water heaters include geysers, instantaneous water heaters including units
    for boiling water, heat pumps, solar systems, induction water heaters and the like (see
    also 6.16.1). electrode water heaters, steam generators and boilers are not included
    (refer to 6.16.7)
    6.16.2.1 All water heaters shall be bonded in accordance with 6.13 and shall
    be protected by earth leakage protection with IΔn not exceeding 30 mA.
    NOTE To mitigate nuisance earth leakage tripping, an additional earth leakage may
    be provided.
    6.16.2.2 Dedicated circuits shall be provided for water heaters and there
    may be more than one water heater on each circuit

Similar Threads

  1. [Question] about connecting geyser controller to plug point
    By SilverNodashi in forum Electrical Contracting Industry Forum
    Replies: 13
    Last Post: 27-Feb-18, 06:16 PM
  2. [Question] Plug circuit works but no neutral return path
    By DavyR in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 25-Nov-16, 08:13 AM
  3. [Question] Plug circuit's neutral wire is 1.5mm, cb amp rating?
    By hartdev@hotmail.com in forum Electrical Contracting Industry Forum
    Replies: 7
    Last Post: 23-Mar-16, 08:14 PM
  4. Maximum overcurrent protection on a plug circuit
    By Dave A in forum Electrical Contracting Industry Forum
    Replies: 33
    Last Post: 28-Feb-14, 03:30 PM
  5. Plug tops and C.O.C.
    By Alan in forum Electrical Contracting Industry Forum
    Replies: 9
    Last Post: 02-Dec-12, 08:40 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •