    Hi it's Shaneo here, I'm an electrical contractor on the South Coast and would appreciate some advice on what size electrical cable to use from the Eskom box to a single phase 63A DB board for a domestic installation (4 bedroom house). The distance from the box to the house is 160m and the cable will be buried. I've been looking at the voltage drop tables but not 100% sure if I'm understanding it correctly. Not sure whether to go with 16mm ECC or 25mm ECC, Thanks.

  2. #2
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,236
    Thanks
    34
    Thanked 304 Times in 258 Posts
    Hi

    I am assuming that the Eskom CB is 63 Amp feeding the installation and that it is not a 80 Amp supply feeding a 63 Amp isolator in the DB.

    I have found that it is best to use SANS 10142 tables to determine the cable distances vs Amps needed especially on single phase .I have attached the page for reference.

    I would go with 25 sqmm
    Attached Files Attached Files

  3. #3
    Junior Member
    Join Date
    Feb 2018
    Location
    umkomaas
    Posts
    13
    Thanks
    4
    Thanked 0 Times in 0 Posts
    Quote Originally Posted by GCE View Post
    Hi

    I am assuming that the Eskom CB is 63 Amp feeding the installation and that it is not a 80 Amp supply feeding a 63 Amp isolator in the DB.

    I have found that it is best to use SANS 10142 tables to determine the cable distances vs Amps needed especially on single phase .I have attached the page for reference.

    I would go with 25 sqmm

    Thank you for your advice GCE, I think I will go with the 25 sqmm cable.

    I have another quoestion related to the same property.....
    As I mentioned, the Eskom box is 160m from the house, but only 10m from the gate and I need to get power to the gate for the electric gate motor. Can I run 2 cables from the Eskom box, one up to the house (160m) to feed the house DB board and one to a weather-proof DB at the gate (10m)? Or do I have to run another 160m of cable back to the gate from the house DB board?
    If I can run a 10m straight from the Eskom box to the gate DB, how would I label the DB's, are they both labelled as main DB's fed from the Eskom box?

  4. #4
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    Quote Originally Posted by shaneo View Post
    Thank you for your advice GCE, I think I will go with the 25 sqmm cable.

    I have another quoestion related to the same property.....
    As I mentioned, the Eskom box is 160m from the house, but only 10m from the gate and I need to get power to the gate for the electric gate motor. Can I run 2 cables from the Eskom box, one up to the house (160m) to feed the house DB board and one to a weather-proof DB at the gate (10m)? Or do I have to run another 160m of cable back to the gate from the house DB board?
    If I can run a 10m straight from the Eskom box to the gate DB, how would I label the DB's, are they both labelled as main DB's fed from the Eskom box?
    Not sure about Eskom ...but i dont believe you can fit additional breakers in the meter box...Run the main cable from the eskom meter box to a weather proof "main DB" inside the property at the gate...fit a breaker for the house and others as required ...earth leakage if you plan to fit a plug etc...then run the cable from the "main DB" to a "Sub DB" inside the house...just a note it might pay you to fit a galv steel steel pipe for the cable... pour a bit of concrete over the steel pipe after installing it and compact the ground as best you can...other wise there is a good chance the cable will be removed shortly after you install it...or make sure the power is ready when you install the first section to the gate...then once the main DB is installed and you can power...dig and lay the rest of the cable...unless of course you live in a secure neighborhood.


    down the road from my house ...the guys installed about about 500 metres of cable half a metre deep and compacted the ground ...next morning...half the cable had been removed and the balance the following night ..they hooked it to a vehicle and pulled it out the ground.

  5. Thanks given for this post:

    shaneo (25-Jun-19)

  6. #5
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,236
    Thanks
    34
    Thanked 304 Times in 258 Posts
    I would take a cable from the Eskom kiosk to my own kiosk and label it as main D/Board.
    From the main DB I could then run a circuit to the gate motor and a 2nd circuit to , what would now be , a Sub DB in the dwelling.

    You would need to look at the cost of the kiosk, isolator and 2 CB's vs running surfix to the gate motor from inside the dwelling.

    Even at 160m the cost may be close to each other and then take in the risk of damage/ theft of the kiosk.

  7. Thanks given for this post:

    shaneo (25-Jun-19)

  8. #6
    Junior Member
    Join Date
    Feb 2018
    Location
    umkomaas
    Posts
    13
    Thanks
    4
    Thanked 0 Times in 0 Posts
    Great thank you for the advice GCE, I think I will go with the 25 sqmm.

  9. #7
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,483
    Thanks
    104
    Thanked 141 Times in 134 Posts
    Where is the meter ? Prepaid in the house or credit meter in Eskom Stubby. If there is a prepaid meter in the house then you will have to run a cable from the house for metering purposes. Doubt very much whether Eskom or your Local Municipal Supplier will give permission to feed the gate from the stubby.

    Cheapest way to wire the gate motor from the house is to make sure the motor unit has a low voltage control board. That way, you could use 0.75mm twin flex in conduit underground for the gate supply from a plugin 18V transformer. As long as there are no lights involved at the gate.

    Derek

  10. #8
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    Quote Originally Posted by Derlyn View Post
    Where is the meter ? Prepaid in the house or credit meter in Eskom Stubby. If there is a prepaid meter in the house then you will have to run a cable from the house for metering purposes. Doubt very much whether Eskom or your Local Municipal Supplier will give permission to feed the gate from the stubby.

    Cheapest way to wire the gate motor from the house is to make sure the motor unit has a low voltage control board. That way, you could use 0.75mm twin flex in conduit underground for the gate supply from a plugin 18V transformer. As long as there are no lights involved at the gate.

    Derek
    150 m of 0.75mm twin flex in a conduit fed from an 18 volt transfomer? eeeeish...i do realise... generally the gate is driven by the battery and not the supply (only use to charge the battery) but that is a long run for 18 v.

    Something else to consider...i would "assume" (and not knowing what the customer requires) that there is a good chance a light could be fitted on the gate posts (LEDs...small power)...the fence could get electrified...security lights or just general light near the gate...CCTV for security near or close to the gate...so a power supply to a nano and switch to wireless link to house...and with homes going the smart route ...you could open and close the gate...switch on the lights etc etc etc.

    As GCE mentioned a floor mounted kiosk on the inside or weather proof DB built into the wall on the inside would be the best route.

    A few things i have learnt about fibre glass weather boxes and DB's ...always paint them other wise they look terrible after a few years and the clear glass door cracks and look like crap...fit a dark tint on the clear section...otherwise they crack...i wouldn't recommend a steel or even S/S because being close to the beach.

  11. Thanks given for this post:

    shaneo (25-Jun-19)

  12. #9
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,483
    Thanks
    104
    Thanked 141 Times in 134 Posts
    As I said, as long as there are no lights involved at the gate.

    I always recommend low voltage for gates. The furthest I've done was 130 meters and the voltage at the gate was 15,8 V ( enough for charging the battery )
    Another advantage is that no weatherproof isolator at the gate motor is needed, whereas with 240 Volt it is a requirement.

    There are many variables, but the main question is .... where is the meter going to be located ? In the house or in the Eskom stubby ?

    If the meter is in the house then the main DB will have to be in the house with a cable from the house to the gate motor.

    If the meter is going to be in the house, then a kiosk close to the gate is not an option.

    Derek
    Last edited by Derlyn; 25-Jun-19 at 08:11 PM.

  13. Thanks given for this post:

    shaneo (25-Jun-19)

  14. #10
    Junior Member
    Join Date
    Feb 2018
    Location
    umkomaas
    Posts
    13
    Thanks
    4
    Thanked 0 Times in 0 Posts
    Thanks to everyone for the advice, will be running a 25 sqmm up to the house and then a surfix back down to the gate as lighting will be required at the gate, and because of gate location, theft or damage to a kiosk or DB is a possibility. Does a 4 sqmm sufix supplied from a 5A circuit breaker sound right? And can I run them in the same trench?

Page 1 of 2 12 LastLast

Similar Threads

  1. Advice - Electrical compliance questions
    By Pieter01 in forum Electrical Contracting Industry Forum
    Replies: 0
    Last Post: 19-Jul-16, 11:16 AM
  2. [Article] Exe cable glands for braided cable
    By Master Electrician in forum Electrical Contracting Industry Forum
    Replies: 0
    Last Post: 26-Aug-10, 02:47 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •