    Electrical certificate of Compliance where there is no supply from municipality

    Hi all, there's a project where they are building low cost houses but there is no electrical network or no supply to to the houses, can one issue a COC for the houses?

  2. #2
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,236
    Thanks
    34
    Thanked 304 Times in 258 Posts
    Hi

    In theory you cannot issue a coc for work that does not have power as you will not be able to carry out all the tests .Any COC with generator is only valid with that generator connected , the minute a different generator is connected your power source has changed and you need to retest.

    Being a government type project - In practice you need to do a coc with generator power so that you can submit with your invoice and get paid. Also make sure that you have a witness from the builder or client that signs off that all the electrical was working. I am assuming they have a practical completion at some stage on a block of houses. State on the COC the make and serial number of the generator to prevent problems later
    If you have a witness then at least later if everything is stolen they cannot turn around and say that they never saw it operational and then try and force you to redo at your own cost.
    The generator may be able to be claimed as a separate cost depending on the contract data and information at tender stage .

    We went through a similar situation at a service center for a municipality - Tested with generator , got consultants out there at night to ensure that everybody witness the exterior lighting was operational around the building etc.
    Years later when they finally got power to site there was not a wire left and they had to pay to have it redone

    Use the COC to cover yourself
    Last edited by GCE; 27-May-19 at 06:08 PM.

  3. Thanks given for this post:

    Dave A (02-Jun-19)

  4. #3
    New Member
    Join Date
    Jan 2017
    Location
    witbank
    Posts
    4
    Thanks
    0
    Thanked 0 Times in 0 Posts
    In this case where the generator is used for a coc, how to get loop impedence and pscc

  5. #4
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,236
    Thanks
    34
    Thanked 304 Times in 258 Posts
    Your loop can be measure but should basically be zero as your neutral earth bridge point will be on the genset
    PSCC - will not be more than 1,5 times the rating of the generator unless the motor is to big for the alternator - Generally if you go over the 1,5 times of a generator rated current the generator will stall which will be the max prospective short circuit current.

    Likewise for inverters etc , they all have electronic cut offs

Similar Threads

  1. [Question] Electrical Certificate of Compliance Number?
    By Herman in forum Electrical Contracting Industry Forum
    Replies: 18
    Last Post: 14-Mar-14, 12:23 PM
  2. Electrical compliance certificate
    By ericlowry in forum Electrical Contracting Industry Forum
    Replies: 14
    Last Post: 23-Jul-13, 08:08 AM
  3. The new electrical certificate of compliance
    By Dave A in forum Electrical Contracting Industry Forum
    Replies: 23
    Last Post: 27-Sep-12, 11:34 AM
  4. What are the Electrical Compliance Certificate Requirements
    By MikeS in forum Electrical Contracting Industry Forum
    Replies: 33
    Last Post: 18-Jun-12, 10:24 PM
  5. electrical certificate of compliance
    By murdock in forum General Business Forum
    Replies: 13
    Last Post: 02-Jul-10, 09:13 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •