    Can someone explain to me why you not allowed to use cabtyre cabling in an electrical installation.

    I have ask many other electrician but no one give me answer that makes sense.

    Thanks in advance

  2. #2
    Bronze Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    193
    Thanks
    5
    Thanked 50 Times in 38 Posts
    The SANS 10142 regulation 6.1.11(pasted below ) does not allow you to use flexible cords in an installation would be the easy answer

    The reason behind it I have always understood the insulation is not the same standard as T&E .
    There are flexible cords that are made to higher standards and could be acceptable in the future.But for the time being 6.1.11 applies


    6.1.11 Flexible cords shall not be used as part of the electrical installation,
    except where
    a) required by the relevant product solely for termination or connection of
    moving parts,
    b) specified in the product standard,
    c) used as single cores in conduits,
    d) used in an authorized wiring system (see 3.5), or
    e) needed for the connection of luminaires, provided that each connection is
    limited to one luminaire and to a maximum length of 3 m.

  3. Thanks given for this post:

    Dave A (15-May-19)

  4. #3
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,695
    Thanks
    545
    Thanked 891 Times in 720 Posts
    Flexible cords can be manufactured to far higher specifications than installation cable such as twin and earth, I think the big problem with flexible cords is that they're fine stranded wiring which requires some type of ferrule when it's terminated. Most terminations in electrical accessories and in DB's are designed for the solid type conductors or coarse stranded type conductors which are found in installation cables and aren't suitable for fine stranded wiring.
    _______________________________________________
    I am special and so is Vanash.
    _______________________________________________

Similar Threads

  1. [Question] Electrical Installation Guidelines
    By ThabiG in forum Electrical Contracting Industry Forum
    Replies: 13
    Last Post: 27-Sep-18, 01:25 PM
  2. Electrical Installation Costs
    By Tracsec in forum Electrical Contracting Industry Forum
    Replies: 29
    Last Post: 04-Oct-16, 09:55 PM
  3. [Article] New electrical installation regulations
    By QUINN in forum Electrical Contracting Industry Forum
    Replies: 12
    Last Post: 11-Jun-14, 03:01 PM
  4. Who may work on an electrical installation?
    By douw in forum Electrical Contracting Industry Forum
    Replies: 37
    Last Post: 16-Apr-10, 11:57 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •