    Earth leakage on machine plugs

    A question for you bright sparks...

    Fitting plugs onto a machine...which has 5 pin 16 amp red plugs...there is no earth leakage on the existing plugs on any of the machines.

    If the plugs are used for components on the machine and next to the machine...heaters... blowers etc?

    The other question...

    When you fit additional breakers...the circuit breakers on the machine are wired in the bottom out the top...how would you connect the new circuit breakers?

  2. #2
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,236
    Thanks
    34
    Thanked 304 Times in 258 Posts
    Hi Ians

    You get a 3 phase socket that you can clock the earth pin and thereby stop a normal 5 pin plug top from fitting - My understanding was that these sockets where for machine type equipment installations and exempt from ELU. I stand corrected
    We were once supplied the plug tops in error and wondered why we could not get them to fit.

    I would keep the CB make the same and wire it the same to prevent confusion when working within the panel.Maybe just stick a label on the panel door "reverse wiring "
    More than likely some strange type breaker - then use a make that the manufacturer allows reverse wiring.

  3. #3
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,648
    Thanks
    3,304
    Thanked 2,676 Times in 2,257 Posts
    Blog Entries
    12
    Quote Originally Posted by GCE View Post
    You get a 3 phase socket that you can clock the earth pin and thereby stop a normal 5 pin plug top from fitting - My understanding was that these sockets where for machine type equipment installations and exempt from ELU. I stand corrected
    Does this help?

    6.16.1.6 Where a socket-outlet in accordance with SANS 164-1, SANS 164-2, SANS 164-3, or SANS 60309-1 and SANS 60309-2 is part of the appliance (built-in), the circuit shall be protected by overcurrent and earth leakage protection (see 6.15.) Socket-outlets in accordance with SANS 164-4 shall have overcurrent protection.

    The implication seems to be if the socket outlet does not comply with any of those standards, the requirement for earth leakage protection may fall away..? Perhaps under the dedicated socket outlet clauses?

    The challenge is whether one falls foul of some other part of the standard.

  4. #4
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    Quote Originally Posted by Dave A View Post
    Does this help?

    6.16.1.6 Where a socket-outlet in accordance with SANS 164-1, SANS 164-2, SANS 164-3, or SANS 60309-1 and SANS 60309-2 is part of the appliance (built-in), the circuit shall be protected by overcurrent and earth leakage protection (see 6.15.) Socket-outlets in accordance with SANS 164-4 shall have overcurrent protection.

    The implication seems to be if the socket outlet does not comply with any of those standards, the requirement for earth leakage protection may fall away..? Perhaps under the dedicated socket outlet clauses?

    The challenge is whether one falls foul of some other part of the standard.
    The other question would be...do the plugs wired "on a machine" fall under the sans or oshact.

    It looks like i am going to have to do my homework.

Similar Threads

  1. Earth leakage even with all appliances/plugs removed
    By BrightSide in forum Electrical Contracting Industry Forum
    Replies: 7
    Last Post: 14-Nov-18, 07:20 AM
  2. Does a stove need to be on an earth leakage?
    By Leecatt in forum Electrical Contracting Industry Forum
    Replies: 63
    Last Post: 23-Jan-18, 08:26 AM
  3. Earth Leakage
    By Gtfast in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 10-May-16, 10:11 PM
  4. Earth leakage
    By Electrix in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 24-Feb-16, 09:10 PM
  5. Earth Leakage
    By Pieter00 in forum Electrical Contracting Industry Forum
    Replies: 13
    Last Post: 27-May-13, 12:03 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •