    Incoming Supply and Prepaid metering.

    I have come across many prepaid meters installed by the municipality that is quite sub-standard. They are mostly mounted next to the existing distribution board. and a piece of concrete plaster knocked out of the wall or a slot cut in the DB cover to route the mains through them. If the mains are too short, an extra piece of wire is joined on and the connection taped up. The part that concerns me most however is the fact that they usually feed the existing main breaker from the load (output) side. Although this is probably not illegal, it is not the conventional way. In my experience the main switch was supplied from the top and then a bridge inserted from the bottom (load) side to supply the rest of the installation on the top (supply side). Most breakers are not marked, so I assume that any side could be used for supply. It seems that the reason they do this is is to save space in very crowded distribution boards. In a few instances I have also come across double pole isolators supplied from the "conventional" load side. Is this practice acceptable? (Reg.6.8.2.3)

  2. #2
    Bronze Member
    Join Date
    Mar 2018
    Location
    Western Cape
    Posts
    120
    Thanks
    11
    Thanked 15 Times in 14 Posts
    Morning Henthal

    This is a very interesting point.

    I don't believe that you would be able to use any side as a 'live' or 'load' side unless clearly indicated by the manufacture.

    I have attached a picture of the inside of a circuit breaker and you will see label 12 which is the bottom is the output/load.

    I know that most breakers don't have live and load on them but they do have a diagram on them and normally numbers, 1 on to then 2 underneath on the diagram and so on.

    Click image for larger version. 

Name:	MCB.jpg 
Views:	216 
Size:	26.7 KB 
ID:	7367

  3. #3
    Junior Member
    Join Date
    Nov 2018
    Location
    Welkom
    Posts
    21
    Thanks
    1
    Thanked 0 Times in 0 Posts
    Thank you SeanM. The interesting part is that I don't think it will make a difference to the tripping. The load or overload will be sensed through the whole conductor, load or supply side. I am more concerned about the ethical issue. We are so used to the conventional wiring that someone may assume a wire on the load side is "dead" with the breaker switched off. I just feel that it is bad practice not to follow convention. Also, I am not sure if all breakers are insensitive to the way you wire them. There may be a technical issue of which I am not aware.

  4. #4
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    Conventions vary from place to place, in SA residential installs it's the norm to have supply at the top and load at the bottom, in the UK for example it's vice versa and in the USA the breakers are often mounted horizontally in 2 columns with the busbar in the centre which is similar to them being supplied from the top in this country. As Sean mentioned, whether it's electrically acceptable to supply a circuit breaker from the top or the bottom would depend on the diagram on the breaker itself and the manufacturers data sheet information, some are designed to have the supply on either side and some only from one side.
    _______________________________________________

    _______________________________________________

  5. #5
    Junior Member
    Join Date
    Nov 2018
    Location
    Welkom
    Posts
    21
    Thanks
    1
    Thanked 0 Times in 0 Posts
    Sorry it took me so long to respond Andy. Yes, I am aware of the trends in the UK and USA. I think the Germans also Use the UK method. The breakers all seem to be versatile and very few are marked to indicate load side. I just do not think that it is sound practice to wire your breakers in opposition to the norm. No matter in which country you are. Reg. 6.8.2,3 seems quite clear on this. If maintenance is performed and the maintenance personnel are not wide awake, nasty accidents can result. Not mentioning expensive damage to test instruments. I think it is poor workmanship to wire in opposition to the norm.

  6. #6
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    The reg states it's not recommended to deviate from the 'norm' of supply at the top and load at the bottom but it can be done if the device manufacturer approves of that wiring orientation, it's labelled accordingly and without visible contradiction.

    I'm not really buying into it being poor workmanship, the counter argument would be it's downright dangerous workmanship by any electrician who damaged his equipment or himself because he didn't test properly for safe isolation before continuing with other tests. There's also an argument that establishing or even favouring local 'norms' like this in the regs could be at least partly responsible for making electricians 'assume' things rather than establishing things beyond doubt by testing.....hence even recommending a norm and then giving acceptable exceptions in the following sentance is part of the problem rather than the solution.

    I'd agree I don't see any reason it should be done in a standard domestic DB but it's fairly common practice in commercial or industrial distribution and control panels and also in internal machine wiring.
    _______________________________________________

    _______________________________________________

  7. #7
    Junior Member
    Join Date
    Nov 2018
    Location
    Welkom
    Posts
    21
    Thanks
    1
    Thanked 0 Times in 0 Posts
    I was specifically referring to domestic installations. I do not think it is good practice to divert from the normal practice just because it is easier and you do not have to extend the wires.
    I do not suffer fools lightly, but at least afford them a fighting chance (referring to assumptions). I think there are very few qualified electricians that had not at one time or another made the expensive mistake of testing Voltage on the Ohms scale. Doing this inadvertently makes it so much worse. I, for one, will stick to the norm.

    Regards
    Henthel

  8. #8
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,484
    Thanks
    104
    Thanked 141 Times in 134 Posts
    Hi Henthal

    In your opening post you mention both a breaker and a main switch. Is the mains an isolator or circuit breaker? We were taught supply in top of circuit breakers but supply in bottom of isolators. Not sure if this is still the norm these days but that's what we were taught as appies in the 70's and I've been doing it like that ever since.

    Derek

Similar Threads

  1. 3 phase metering
    By murdock in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 11-May-19, 07:41 PM
  2. No incoming earth again (and again, and again and again )
    By skatingsparks in forum Electrical Contracting Industry Forum
    Replies: 4
    Last Post: 14-Nov-18, 09:05 AM
  3. Amp rating of incoming supply breaker
    By Gnome in forum Electrical Contracting Industry Forum
    Replies: 8
    Last Post: 05-Jun-17, 07:45 PM
  4. Incoming supply
    By Leonsparky in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 10-Aug-16, 10:42 PM
  5. Incoming/Outgoing E mail settings ?
    By HR Solutions in forum General Chat Forum
    Replies: 15
    Last Post: 26-Sep-13, 09:57 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •