    Plastic switch covers.

    If an electrical installation has no earth wire to light switches and the conduit in older installations do not provide an efficient earth, is it accepted legal practice to have plastic switch covers with plastic screws, thus insulating the switch and receptacle from human contact?

  2. #2
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,247
    Thanks
    34
    Thanked 304 Times in 258 Posts
    There was a time period around 2001 that you did not need to install an earth wire to a light switch if it was PVC with pvc screws.
    It only lasted a year or two and then scrapped.

    If I was doing a COC on the installation you describe I would assume it was done within the time period that the metal conduit was used as an earth conductor and would therefore ensure that there is an earth at the light switch.
    Often you can give the locknuts a turn and get to your readings

    It is cheaper to quote the client now for separate earth and install then have a different opinion ( read AIA test) and be forced to do at your own cost later.

    We ensure that there are earth wires at each point , also maybe the reason we don't get much COC type inspection work.
    I prefer protecting my licence then end up in arguments

  3. #3
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,660
    Thanks
    3,307
    Thanked 2,676 Times in 2,258 Posts
    Blog Entries
    12
    I've understood the situation to be exposed conductive parts need to earthed, and that if the component has a earthing terminal, it must be connected to earth (some small print, particularly relating to safety supplies applies).

    It had me looking at light switch chassis, and the metal ones in my store have an earth terminal. The plastic chassis switches (unsurprisingly) do not.

  4. #4
    Bronze Member
    Join Date
    Mar 2018
    Location
    Western Cape
    Posts
    120
    Thanks
    11
    Thanked 15 Times in 14 Posts
    Morning All

    Please remember that it is illegal to use the metal Conduit as an earth.

  5. #5
    Junior Member
    Join Date
    Nov 2018
    Location
    Welkom
    Posts
    21
    Thanks
    1
    Thanked 0 Times in 0 Posts
    Thank you all for your input. SeanM raises an interesting point that is another area shaded in grey. Many old installations made use of the well installed steel conduit (in the day of artisans) before an earth conductor became compulsory. In many houses and blocks of flats, you will find this. The way I read the Regulations, this is acceptable on installations completed before 2008, with the proviso that acceptable earth continuity readings are obtained during tests. This also raises another problem when it comes to replacing a socket outlet. The new plastic outlets have no continuity from the earth terminal to the mounting plate. You must thus install a flying earth lead that is lugged and properly secured to the wall box to ensure a proper earth. Your valuable comments will be appreciated.

  6. #6
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,247
    Thanks
    34
    Thanked 304 Times in 258 Posts
    Hi

    I pulled out the oldest regulations that I have which is SABS 0142-1 valid from date of approval 1 November 2001 .
    In that edition 6.12.1.3 already stated that a wireway may not be used as an earth conductor.
    I cant find an older edition - I think that is more a prior to 1994 than 2008 with regards to a separate earth.
    I have a feeling that when I wrote reg's in 1988 a separate earth was already a requirement - I don't ever remember using conduit as an earth.
    Yes if the building is old and the conduit is still the screw type the chances are that the regulation at time of installation allowed the conduit to be an earth and if your readings are acceptable you could sign off.
    We did put in flyleads from the steel box to the earth terminal in old installations , generally factories where the conduit is still good.
    We have had a couple of old houses where the conduit has rusted through under the ground and had no earth , back in the day when I would tackle that sort of work.
    Now I refuse to sign off without installing earth wires.

    I have had conversations with AIA's where they read the reg's as saying if work has been done on a circuit then the complete circuit should be upgraded to the new regulations.The definition of electrical installation work includes repairs and maintenance.

  7. Thanks given for this post:

    Leecatt (03-Feb-19)

  8. #7
    Junior Member
    Join Date
    Nov 2018
    Location
    Welkom
    Posts
    21
    Thanks
    1
    Thanked 0 Times in 0 Posts
    Thank you GCE, I firstly want to ensure you that I am not trying to find loopholes in the system. I just want to confirm what the inspection authorities class as "reasonably safe" in a fairly old installation. In the ECB test report attached to the CoC, page 4 point 13 allows a choice of (a) or (b) in the answer and point (b)reads, and I quote: - In the case of installations that existed before the publication of this edition of SANS 10142-1, the installation complies with the general safety requirements in this part of SANS 10142-1 and is reasonably safe. - This statement forms part of the test report and my interpretation is that if your test results comply, the installation is reasonably safe. I can not see how a person can charge a customer for a complete rewire, if the earthing is within the required parameters. That is also what prompted my initial question regarding switches. Surely a plastic switch with a plastic cover and no exposed metal parts is "reasonably safe". The previous edition of SANS 10149-1 to my knowledge was published in 2008-2009. Please correct me if I am wrong on this point.

  9. #8
    Bronze Member
    Join Date
    Mar 2018
    Location
    Western Cape
    Posts
    120
    Thanks
    11
    Thanked 15 Times in 14 Posts
    Hi Henthal

    With regards to your question on a plastic light switch this is safe.

    Take the plastic LED down light unit no earth required.

  10. #9
    Silver Member
    Join Date
    Jul 2008
    Location
    Germiston, South Africa
    Posts
    397
    Thanks
    24
    Thanked 47 Times in 43 Posts
    The answer is quite straightforward when you look at the whole of SANS 10142.
    First of all at the beginning of SANS 10142

    1.2.Aspects covered by this part of SANS10142.
    This part of SANS 10142 covers
    I) replacement or maintenance of components


    From this short sentence it is clear that any replacement or maintenance of any component of the electrical installation must be done under the current version of SANS 10142

    According to the latest version of SANS10142:
    6.12.1.3 A wireway shall not be used as an earth continuity conductor
    Last edited by Leecatt; 03-Feb-19 at 06:32 AM. Reason: Adjustments of paragraghs
    To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

  11. #10
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,247
    Thanks
    34
    Thanked 304 Times in 258 Posts
    Hi

    This thread has made me do some serious thinking.
    We need to remember that the OHSA also has a play on the regulations and the way we conduct our business .

    My understanding of reasonable safe is that it must comply to section 5 , fundamentals , of the code .
    So metal conduit on an old installation and now fitted with PVC switches would not need to have an earth wire as I read it .

    But as pointed out by Leecatt above any replacement etc must comply to the latest version at the time.Pvc switches where not available at the time of metal conduit and it is therefore assumed that it was done much later. ( the majority of PVC switches came out after the change in reg's that stated earth wire must go to the earthing terminals of all permanently connected electrical equipment and appliances. My memory anyway)

    If I look at the latest regulations I cannot come up with a reason to run an earth wire to a light switch that is PVC without an earth terminal , has pvc conduit and pvc wall box.
    But - If I look at the OHSA , electrical machinery regulations , section 18 Earthing

    Earthing
    18. ( 1) An employer or user shall cause -
    (b) all accessible metallic parts of electrical machinery that, though normally
    not forming part of an electrical circuit, may become live accidentally, to be
    protected by an insulating covering or to be otherwise enclosed or to be
    earthed and the resistance of the earth continuity path shall not exceed
    0,2 ohm, except-
    (iv) metalwork of fixed electrical machinery where such metalwork is
    more than 2.4 m above the floor: Provided that this exception shall
    not apply where such metalwork is situated in any position likely to
    become damp, or in an elevator shaft, or near rotating machinery,
    or in contact with a wall, ceiling or other support constructed of or
    covered with conducting material


    To me , and maybe I am taking it out of context , I need to earth the metal box/ conduit as it is in contact with the wall , and to bring it into context the conduit may be above 2,4m - On an old installation I suppose that means that it must be earth but not necessarily have an earth wire.

    In answer to Henthel's question "I can not see how a person can charge a customer for a complete rewire, if the earthing is within the required parameters" The introduction of SANS 10142 and the OHSA gives me a chance to insist on more than the basic requirements .I have pasted 5 pieces below which to me would be relevant when trying to persuade the client to accept my insistence on installing separate earth wires.I know that there is a chance of a hot connection which may cause a smoldering of the switch hidden behind a curtain that sets the fire off or the wiring burning back in the conduit and not tripping the supply until the roof space starts smoldering.
    May sound extreme but I watched my folks lose there entire house and contents in the space of 30 minutes due to a short on an electric blanket while they were in the room.Made me rethink on what is required by regulation and what is required from me as a responsible person signing off reasonable safe.

    As a responsible person signing the COC I need to be 100% sure in myself that what I am declaring as reasonable safe is definitely so .There can be no doubt within myself otherwise I will not be able to convince somebody else in the event of a problem that I did everything possible to prevent a problem.If that doubt is there I then run the risk of being prosecuted under the OHSA.

    Think it a reason that I don't do COC type work on existing installations as we just quote on the work , to do it as we see correctly , only to go back later to see the disaster. If we do COC type inspections we will only do for the buyer as he understands whereas the seller wants as cheap as possible.


    Extracts from SANS 10142-1
    Compliance with this document cannot confer immunity from legal
    obligations


    The aim of this part of SANS 10142 is to ensure that people, animals and
    property are protected from hazards that can arise from the operation of an
    electrical installation under both normal and fault conditions. An electrical
    installation has to provide protection against:
    – shock current,
    – overcurrent,
    – fault current,
    – overvoltage,
    – undervoltage,
    – excessive temperatures, and
    – electric arcs.


    This part of SANS 10142 is concerned with ensuring the basic safety of
    electrical installations. To ensure the protection of people, animals and
    property and the proper functioning of an installation, the designer of an
    electrical installation should be aware of:
    a) the characteristics of the power supply,
    b) the nature of the demand, and
    c) the operating environment of each part of the installation


    Extract From General Administrative regulations
    9. General duties of employers and self-employed persons to persons other than their employees

    (1) Every employer shall conduct his undertaking in such a manner as to ensure, as far as is reasonably practicable, that persons other than those in his employment who may be directly affected by his activities are not thereby exposed to hazards to their health or safety.

    (2) Every self-employed person shall conduct his undertaking in such a manner as to ensure, as far as is reasonably practicable, that he and other persons who may be directly affected by his activities are not thereby exposed to hazards to their health or safety.


    Extract from General Safety Regulations
    2. (1) Subject to the provisions of paragraphs (f), (g), (h) and (i) of regulation 5 of the General Administrative Regulations published under Government Notice R. 2206 of 5 October 1984, every employer and every user of machinery shall make an evaluation of the risk attached to any condition or situation which may arise from the activities of such employer or user, as the case may be, and to which persons at a workplace or in the course of their employment or in connection with the use of machinery are exposed, and he shall take such steps as may under the circumstances be necessary to make such condition or situation safe

Page 1 of 2 12 LastLast

Similar Threads

  1. Plastic bag money
    By duncan drennan in forum South African Politics Forum
    Replies: 1
    Last Post: 12-Nov-07, 09:48 PM
  2. Turn plastic to oil - with a microwave!
    By duncan drennan in forum Technology Forum
    Replies: 3