Results 1 to 7 of 7

Thread: Fault finding

  1. #1
    Full Member
    Join Date
    Mar 2018
    Location
    Western Cape
    Posts
    74
    Thanks
    9
    Thanked 10 Times in 9 Posts

    Fault finding

    Greetings

    I have a customer that called as his main breaker (3 phase 45 amp) trips intermittently.

    So I went out balanced the phases and grade the circuit breakers correctly (breaker from main DB feeding sub DB was the same size as the main breaker)

    Ciruits seem clear when tested.

    I left and the same fault persists, advice please?

  2. #2
    Platinum Member
    Join Date
    Apr 2010
    Location
    KZN
    Posts
    1,770
    Thanks
    80
    Thanked 155 Times in 134 Posts
    try a D cure or curve 1 breaker...if that doesnt work then install a PQA and see what time it trips and why it is tripping...overload or fault.

    if you dont have a PQA...then its just a guessing game.

  3. #3
    Full Member
    Join Date
    Mar 2018
    Location
    Western Cape
    Posts
    74
    Thanks
    9
    Thanked 10 Times in 9 Posts
    Thank you

  4. #4
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,698
    Thanks
    546
    Thanked 892 Times in 721 Posts
    Is it normal domestic circuits like stove, geyser, plugs and lights?
    _______________________________________________
    I am special and so is Vanash.
    _______________________________________________

  5. #5
    Full Member
    Join Date
    Mar 2018
    Location
    Western Cape
    Posts
    74
    Thanks
    9
    Thanked 10 Times in 9 Posts
    Hi Andy

    The circuits are ups, plugs, lights and aircons. It is a shop at the Waterfront.

  6. #6
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,698
    Thanks
    546
    Thanked 892 Times in 721 Posts
    Eek, 45A per phase isn't much if it's a commercial premises with geyser, air con, probably lots of LED lights with horiffic inrush currents and power factor and gawd knows what else they're plugging in.

    If you don't have access to a PQA or data logger you can prove whether it's a fault or a general overload condition by installing a second temporary 'main breaker' downstream from the existing one and make it a higher current rating. In this case I'd probably go with a 60A breaker but obviously whether this is a viable option or not depends on whether there's space in the DB. If the 60 Amp breaker stays up next time the power trips then it's an overload problem, if it trips simultaneously along with the 45A main breaker then there's a very good chance it's an intermittant fault either somewhere on the installation or on one of the items plugged in.
    _______________________________________________
    I am special and so is Vanash.
    _______________________________________________

  7. Thanks given for this post:

    SeanM (04-Jan-19)

  8. #7
    Full Member
    Join Date
    Mar 2018
    Location
    Western Cape
    Posts
    74
    Thanks
    9
    Thanked 10 Times in 9 Posts
    Morning Andy

    This is really good advise, I would never of thought of putting a secondary breaker in.

    An update I changed the main breaker to a 50 amp 3 phase (the main cable is a 10mm) , I am not a fan of just increasing breaker sizes.

    And to date no tripping

Similar Threads

  1. [Opinion] Cable Fault Locators
    By ACEsterhuizen in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 09-Feb-17, 07:49 AM
  2. Debt not my fault - what do I do ?
    By litepod in forum National Credit Act Forum
    Replies: 9
    Last Post: 14-Jan-12, 07:05 PM
  3. fault level
    By murdock in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 14-Sep-11, 02:44 PM
  4. HELP!! Who is liable for electrical fault
    By TemplerML in forum Electrical Contracting Industry Forum
    Replies: 9
    Last Post: 22-Jan-10, 06:54 AM
  5. It's not my fault!
    By Dave A in forum South African Politics Forum
    Replies: 3
    Last Post: 09-Dec-08, 01:43 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •