Results 1 to 5 of 5

Thread: PVC flexible conduit

  1. #1
    New Member
    Join Date
    Mar 2015
    Location
    windhoek
    Posts
    3
    Thanks
    0
    Thanked 0 Times in 0 Posts

    PVC flexible conduit

    I recently completed my U/S inspection and certification of a three phase industrial/commercial installations, and according to my trainer the use of pvc flexible conduits on a permanent installation was never approved, however we have a general regulation on flexible conduits in SANS 10142, clause 6.5.4.2.
    I would like to know the specs of this item from SANS 61386-23, if anyone with this document can at least e-mail me the section prohibiting the use of flexible pvc conduits in a permanent installation.

  2. #2
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,248
    Thanks
    34
    Thanked 304 Times in 258 Posts
    Hi

    With regards to installation of flexible conduit not allowed in a permanent installation - That is the first time I have heard that one - Makes me nervous that somebody makes that statement .We are not major users of flexible conduits but there are places that it comes in useful.
    6.5.4.2 c - states unless it has been designed for that purpose

    I know that when Clipsal first introduced flexible conduit there were different grades for different uses , like in roof spaces and then a stronger flexible conduit for use in concrete decks.If the manufacturer states that the flexible conduit is suitable for concrete work , or under plaster then I do not see a problem with it and to me it would pass 6.5.4.2 c .
    6.16.1.11 refers to flexible conduit being allowed for stationary appliances

    Would be interested to know who told you it is not allowed and what regulation he is using to make that statement.

    6.5.4 Flexible conduit
    6.5.4.1 Earthing
    Metal flexible conduit, even if insulated, shall be connected to earth but shall
    not be used as an earth continuity conductor.
    6.5.4.2 Installation
    Flexible conduit shall
    a) use only appropriate glands and terminations,
    b) not be so bent that it could open or be damaged when it is strained in
    normal use, and
    c) not be buried in plaster, screed, or concrete, unless it has been designed
    for that purpose.


    6.16.1.11 Flexible conduit may be used for the final connection to a fixed or
    stationary appliance but may not be used as the final connection to a
    portable appliance, unless it has been authorized for this use.



    Sans 61386-23 refers to the IEC 61386-1 (pasted below ) - The 61386 code refers to manufacturing tests etc that the conduit needs to pass to enable the SANS mark.
    The IEC code is freely available on the net

    This part 23, which specifies particular requirements for flexible conduit systems, is to be used
    in conjunction with IEC 61386-1, Conduit systems for cable installations – Part 1: General
    Requirements 1, and its amendments. It was established on the basis of the first edition (1996)
    of that standard and its amendment 1 (2000).

  3. Thanks given for this post:

    Dave A (02-Dec-18)

  4. #3
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,924
    Thanks
    576
    Thanked 934 Times in 755 Posts
    It's news to me as well but I suspect he's refering to 6.16.1.11. I don't use the domestic 'spreg' type flexible conduit but I do use large quantities of 316 stainless steel Copex on specialised commercial installations sometimes.
    _______________________________________________

    _______________________________________________

  5. #4
    Full Member smithers's Avatar
    Join Date
    Sep 2012
    Location
    cape town
    Posts
    58
    Thanks
    0
    Thanked 11 Times in 11 Posts
    i am not in the electrical field, but have seen plenty homes built in our area that use Builders PVC Conduit 20mm that gets laid before concrete is poured and used to run wiring up the brick wall construction. I know the Overberg has had some real dodgy home build in the past years, but inspectors now are pretty ruthless on rules being adhered to (some of the electricians are not certified to pass CoC).

    this topic certainly helps me making sure what should be used when i start on the building of a new structure on my plot

  6. #5
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    Flexible conduit...you get a white one and a grey one.

    The white one is absolute rubbish...you can squeeze it flat with your hand and generally will collapse during installation and splits after a short time while.

    The grey one on the other hand is the right stuff...i believe it is supplied by hellerman...i give that stuff a thumbs up...first i am hearing that you cant use it...someone would be failing lots of my projects if that is the case.

Similar Threads

  1. [Question] flexible cables
    By murdock in forum Electrical Contracting Industry Forum
    Replies: 18
    Last Post: 11-Sep-23, 07:52 AM
  2. Too many cables in conduit
    By skatingsparks in forum Electrical Contracting Industry Forum
    Replies: 31
    Last Post: 12-Mar-19, 09:02 AM
  3. [Question] Flexible conduit
    By Tang in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 02-Sep-18, 07:11 PM
  4. [Opinion] FLEXIBLE LOAN OFFER
    By luisgomezloanfirm1 in forum Scam Alert Forum
    Replies: 4
    Last Post: 12-Feb-18, 10:28 AM
  5. Anywhere where I may find flexible drill bits?
    By RohanB in forum General Chat Forum
    Replies: 5
    Last Post: 26-Jul-11, 08:36 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •