    Hi

    We are having a look at a COC inspection on a commercial building - There is a 400 Amp settable CB with a length of 185 sqmm cable feeding out.
    The breaker can be set down to 350 Amp and the cable will be protected. SANS10142-1 table 6.4 pg 99
    To me it is all legal and can be signed off
    The argument in the workshop is that it is incorrect and that the cable should be sized to the maximum rating of the C/breaker .The setting down will be used purely to control the loading of the center.

    Interested to hear what the feeling is on the forum.

  2. #2
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    I would agree that the cable should be sized to the max rating...however...certain application due to design...fault levels or future upgrades could require a bigger breaker.

    This could help solve the problem

    https://www.schneider-electric.ca/en/faqs/FA103647/

  3. Thanks given for this post:

    GCE (25-Oct-18)

  4. #3
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    If the circuit breaker is not in the customers DB (accessible by a skilled person only) I'd say it was compliant if set correctly. If it's in the DB and accessible to the customer then, as per Ians link I'd say it was compliant if the adjustment panel on the breaker is sealed and required a tool to open and adjust. We usually use the old style wire and lead crimp tags because we have a tool that imprints an specific ID symbol into the tag but I guess even a cable strap would suffice.
    _______________________________________________

    _______________________________________________

  5. Thanks given for this post:

    GCE (25-Oct-18)

  6. #4
    Full Member
    Join Date
    Oct 2012
    Location
    Durban
    Posts
    66
    Thanks
    0
    Thanked 5 Times in 4 Posts
    It will be interesting to see all the responses. I have had this in the past and am uncomfortable with a C/B which has been adjusted to accommodate the cable size. I have in the past come across instances where overloads have been turned up beyond the motor rating by 'electricians' to prevent the overload from operating instead of finding out the reason for the trip and it would be safe to say that there is no reason why this wouldn't occur with a C/B either.

  7. #5
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    I think you can't stop stupidity or malice by legislation. A qualified sparky has got a duty of care not to exceed cable or motor current limits, if he ignores that duty of care he needs to be held accountable.
    _______________________________________________

    _______________________________________________

  8. #6
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    Quote Originally Posted by RegElec View Post
    It will be interesting to see all the responses. I have had this in the past and am uncomfortable with a C/B which has been adjusted to accommodate the cable size. I have in the past come across instances where overloads have been turned up beyond the motor rating by 'electricians' to prevent the overload from operating instead of finding out the reason for the trip and it would be safe to say that there is no reason why this wouldn't occur with a C/B either.
    People disconnect the earth wire to prevent the e/l unit from tripping...people replace 20 amp breaker with 30 amp breakers because the 20 amp trips when they plug in a kettle...toaster and iron...or back in the day when big bang aircons started...they would trip breakers... so instead of installing a 20 amp D cure or curve 1 breaker...they didnt know any better ...so a 30 or 35 would do the trick...but that is not what i have seen burn houses down.

    the last granny flat i visited after it almost burnt to the ground...the fire started at a connector block below the aircon ...used to extend the cable to reach a plug 5 metres away...lucky for the person sleeping in the room...the unit exploded which blew it across the room...waking the lady up...which saved her life.

    i find when you get to the bigger stuff like adjustable breakers...the level of competency of the electricians working in that area is higher...we have a respect for the stuff because if you work in that kind of environment...good chance you have already seen the result of dumb actions...if you are still alive.

    make no mistake there are way too many unskilled and inexperienced people working out there...we just have to do our best to stay on the straight and narrow.

  9. #7
    Junior Member
    Join Date
    Sep 2018
    Location
    KZN
    Posts
    16
    Thanks
    0
    Thanked 0 Times in 0 Posts
    If a fuse blows, fit a bigger one? Wondering how many fires resulted.

  10. #8
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,236
    Thanks
    34
    Thanked 304 Times in 258 Posts
    Hi

    Still busy contemplating the dynamics around settable circuit breakers and found this under fundamentals 5.4.3 - Thought the "likely to be subjected to" kind of throws a curved ball when we basically expect everybody after us to be careless .
    Was extremely happy to find 6.7.2.4 which gives us some protection if we do as Andy and Ians suggested further up


    [B]5.4.3 Current[/B]
    The equipment shall be suitable for operation at the maximum steady
    (r.m.s.) current to which it is likely to be subjected. It shall also be able to
    carry the current that is likely to flow under abnormal conditions and for the
    period that the current is likely to flow.
    NOTE The period that an abnormal current will flow is equal to the operating time of
    any protective device


    [B]6.7.2.4 [/B]Protective devices that have adjustable overload settings shall only
    be used if the means of adjustment is not accessible without the use of a
    tool and the adjustment can only be made by means of a tool.

  11. Thanks given for this post:

    AndyD (14-Nov-18)

  12. #9
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    Quote Originally Posted by AndyD View Post
    I think you can't stop stupidity or malice by legislation. A qualified sparky has got a duty of care not to exceed cable or motor current limits, if he ignores that duty of care he needs to be held accountable.
    which country do you live in?

  13. #10
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    Quote Originally Posted by GCE View Post
    Hi

    Still busy contemplating the dynamics around settable circuit breakers and found this under fundamentals 5.4.3 - Thought the "likely to be subjected to" kind of throws a curved ball when we basically expect everybody after us to be careless .
    Was extremely happy to find 6.7.2.4 which gives us some protection if we do as Andy and Ians suggested further up


    [B]5.4.3 Current[/B]
    The equipment shall be suitable for operation at the maximum steady
    (r.m.s.) current to which it is likely to be subjected. It shall also be able to
    carry the current that is likely to flow under abnormal conditions and for the
    period that the current is likely to flow.
    NOTE The period that an abnormal current will flow is equal to the operating time of
    any protective device


    [B]6.7.2.4 [/B]Protective devices that have adjustable overload settings shall only
    be used if the means of adjustment is not accessible without the use of a
    tool and the adjustment can only be made by means of a tool.
    thank goodness we live in an era where technology has progressed so far that it is possible to to take pics and time stamp them with a hand held device which you carry in your pocket on a daily basis...set the device...take a pic... record it on a COC and walk away.

Similar Threads

  1. Circuit Breaker faulty?
    By Melchior in forum Electrical Contracting Industry Forum
    Replies: 7
    Last Post: 09-Mar-17, 11:18 PM
  2. Is no service a contract breaker?
    By insulin in forum Marketing Forum
    Replies: 7
    Last Post: 10-Mar-14, 06:21 PM
  3. Circuit Breaker tester
    By ELECT 1 in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 21-Dec-13, 12:17 AM
  4. buzzzing circuit breaker
    By murdock in forum Electrical Contracting Industry Forum
    Replies: 4
    Last Post: 08-Mar-11, 10:47 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •