    New dwelling 170m away from main supply

    Hi guys,
    Wondering if you could give me your 2 cents worth?
    I have a client who has a farm with 3 phase power.
    He wants to build a staff cottage and power a couple of water pumps 170m away from the main installation and nearest DB.
    The cottage will employ an electric geyser, and possibly an electric oven, but I will strongly advise gas to save on power consumption. I would be looking at around 40A single phase worst case scenario needed on the cottage end.
    After consulting my regs book am i right in saying that if I run single phase this distance, I would require a 35mm 2 core armoured cable to do the job.
    If I was to supply 3 phase across this distance then I would only need to run a 10mm 4 core armoured cable to supply 20 amps/ phase, which, if loaded correctly, should supply the necessary power to the cottage and run the pumps. (I don't think the pumps will be 3 phase).
    Does this sound about right?
    Does anyone have a better idea of how to get power there?
    Many thanks
    We are not human beings undergoing a spiritual phase.....we are spiritual beings undergoing a human phase....

  2. #2
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,236
    Thanks
    34
    Thanked 304 Times in 258 Posts
    Hi

    The other way is to do a step up cable step down transformer - The distance and amperage will not warrant the cost

    The 10sqmm x 4c should be sufficient to run 20 amps but be careful on the pump size and start arrangement - A motor, direct on line start up current, can be 6 times higher then run current - It can cause a problem.If I was quoting I would allow for a VSD and if the client does not want the VSD and is prepared to take the chance then so be it - When the motor burns out at least you covered yourself.

    People always forget start up current when sizing long lengths of cables and generators for motors.

  3. #3
    Full Member
    Join Date
    Jun 2012
    Location
    Plettenberg Bay
    Posts
    69
    Thanks
    1
    Thanked 17 Times in 13 Posts
    Yeah, I agree, the step up step down would not warrant the cost to the client.
    I will get specs of the pump from my client before I advise anything though.
    Thanks for your input
    We are not human beings undergoing a spiritual phase.....we are spiritual beings undergoing a human phase....

Similar Threads

  1. House DB main switch
    By Slow Blow in forum Electrical Contracting Industry Forum
    Replies: 21
    Last Post: 26-Jun-16, 11:25 PM
  2. max number of people per dwelling
    By murdock in forum General Chat Forum
    Replies: 5
    Last Post: 10-Jul-11, 06:48 PM
  3. Main Switch?
    By Sparks in forum Electrical Contracting Industry Forum
    Replies: 0
    Last Post: 08-Feb-11, 10:16 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •