    Cooker connected with a length of 6mm Surfix

    I don't do much domestic work but I have found cookers connections like this. Is this right?

  2. #2
    Bronze Member
    Join Date
    Mar 2018
    Location
    Western Cape
    Posts
    120
    Thanks
    11
    Thanked 15 Times in 14 Posts
    Morning Darking

    One would need further info to answer you query accurately.

    What size is the cooker?
    What is the size of the breaker?
    Is there a isolator within 1,5m?
    Is there a stove cooker coupler or is the circuit on a earth leakage?

    6mm can handle 40 amps

  3. #3
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,648
    Thanks
    3,304
    Thanked 2,676 Times in 2,257 Posts
    Blog Entries
    12
    Just trying to gauge your area of interest in asking...

    As opposed to the commonly found 6mm house wire in flexible conduit?

  4. #4
    Junior Member
    Join Date
    Sep 2018
    Location
    KZN
    Posts
    16
    Thanks
    0
    Thanked 0 Times in 0 Posts
    The Cooker is 45Amp maximum demand and is supplied by a 30 Amp breaker, connected through an ELC and the isolator is within 1.5 meters. Long ago when I was an apprentice I supplemented my meagre pay by repairing old stoves and washing machines and the cooker units had house wire in metallic flexible conduit. Surfix cable could be subject to damage by flexing when the unit is moved so surely this is not fit for purpose?

  5. #5
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    Some people connect stoves with a 15 amp plug socket.

    It depends on the application.

    There is a list of variables for stove/cooker connections.

Similar Threads

  1. [Question] Connected Advertising / email from: connected010@telkomsa.net
    By padjakkels in forum Scam Alert Forum
    Replies: 2
    Last Post: 05-Oct-16, 02:33 PM
  2. surfix
    By bergie in forum Electrical Contracting Industry Forum
    Replies: 8
    Last Post: 22-Oct-14, 01:06 AM
  3. Invoice length?
    By league_of_ordinary_men in forum Tax Forum
    Replies: 6
    Last Post: 16-Oct-13, 04:59 PM
  4. Retrenchment - Length of Service
    By Buddyt in forum General Business Forum
    Replies: 3
    Last Post: 11-Nov-08, 07:50 AM
  5. you have to be connected to enjoy the fruits of injustice.
    By Dave A in forum General Business Forum
    Replies: 2
    Last Post: 26-Jun-08, 08:44 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •