    Eco friendly installations

    Hi ,to the members in the forum. I would like some advice in the following matters.

    1 How does one deal with the fact that , quite a number of light switches, and 220v led downlighters with built in electronics . Are contstucted of plastic , and have no earthing points. Do we simply run the earth point to the junction box and terminate ,or connect to the wall box if metal.

    2 I have to make provision for two eco ovens that have been purchased, they have a max rating of 2.5kw each
    And are already wired for connection to standard 3 pin plug for connection to 15 amp. How would you suggest this gets wired and would you use a circuit breaker for each oven

    3 What would be the recommended number of 15 amp socket outlets per circuit breaker .

  2. #2
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,246
    Thanks
    34
    Thanked 304 Times in 258 Posts
    Hi

    I would connect to the wall box if metal - You still need the earth to be at the point of consumption for in case the switch is ever changed to a metal plate.

    A 2,5KW oven will draw 10 Amps and 2 ovens on the same circuit may exceed your C/Breaker size - It would be advisable to have 2 circuits - It is a borderline case

    There is no recommendation for the number of socket outlets on a circuit and it all depends on the installation and usage.

    SANS 10142 6.15.2.2 - The anticipated load of a circuit that feeds socket outlets shall not exceed 5 KW .

  3. Thanks given for this post:

    Lmstrade (04-Sep-18)

  4. #3
    New Member
    Join Date
    Aug 2018
    Location
    Johannesburg
    Posts
    3
    Thanks
    1
    Thanked 0 Times in 0 Posts
    Thanks for advice GCE

    Two further questions if I may .

    1. When connecting a cable run to a group of led downlights in a room the connectors on the LED are not big enough to loop in two cables (1.5mm TWE ) .
    a. Solution : a Junction box to loop in the TWE at every LED downlight ,then a smaller gauge more flexible wire pigtail to the light ( 350mm of Cabtyre , or other ??? )
    b. any other ideas or solutions ????

    2. For the ovens , running two 20 Amp C/ Breakers , to a single 15amp 3 pin dual outlet at rear of OVENs each socket individually wired with its own 2.5mm TWE cable to the respective C/breakers
    Have you any thoughts on wiring the Oven isolator switch, that wouldnt require a whole bundle of wires running up and down conduit..

  5. #4
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,246
    Thanks
    34
    Thanked 304 Times in 258 Posts
    Hi

    Down lighters - We run the wiring to 5 Amp socket outlets in the ceiling space from the light switch - Install a 5 amp cord set on the down lighter and plug in.

    With the ovens I would stick to what you are doing - Saying that , have you tried running the ovens and seeing what load they draw - Are there different function and will both ovens draw maximum load at the same time. You might get away with one circuit. It appears a borderline case

Similar Threads

  1. Replies: 0
    Last Post: 14-Apr-15, 08:49 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •