    10mm SWA n parallel as sub main?

    Hi. Can anyone see a problem with having 2 x 4 core 10mm swa as an 80 amp sub main supply. I know 10mm 4 core can take 62 amps. If run together in parallel from the same 80 amp mccb breaker to the same sub main switch in the the same sub db board with a 10mm c.p.c. can anyone see a problem with that? Its an existing installation. At the moment there is no 10mm earth so I intend to add that as the earth fault loop reading is a little high. Advise please.

  2. #2
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,924
    Thanks
    576
    Thanked 934 Times in 755 Posts
    From memory, there is a reference to this somewhere in the regs which I don't have available to check at the moment. It was in amendment 6 or 7 maybe and in the cable current capacity section. It says something along the lines of as long as the cables are same cunductor size and conductor material and insulation material and they follow the same route (same length) and installation method, they must be supplied from the same place in the DB, there's no spurs or tees then yes, you can use parallel cables to carry the load. I can't remember off hand if there's a derating factor to be applied... I'd have to check tomorrow.
    _______________________________________________

    _______________________________________________

  3. #3
    Bronze Member
    Join Date
    Mar 2018
    Location
    Western Cape
    Posts
    120
    Thanks
    11
    Thanked 15 Times in 14 Posts
    Hi Skating Sparks

    There are no issues with doubling up on your cable.

  4. #4
    Junior Member
    Join Date
    Apr 2014
    Location
    Westrand
    Posts
    23
    Thanks
    6
    Thanked 2 Times in 2 Posts
    No problem as long as they are EXACT same length.

    Sent from my SM-N950F using Tapatalk

Similar Threads

  1. [Question] House main DB Modifications?
    By desertburner in forum Electrical Contracting Industry Forum
    Replies: 8
    Last Post: 20-Apr-18, 01:15 PM
  2. House DB main switch
    By Slow Blow in forum Electrical Contracting Industry Forum
    Replies: 21
    Last Post: 26-Jun-16, 11:25 PM
  3. Main Switch?
    By Sparks in forum Electrical Contracting Industry Forum
    Replies: 0
    Last Post: 08-Feb-11, 10:16 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •