    New sockets - sans 164-2

    Has anyone/everyone started using the new S.A. sockets (like mobile phone charger but with earth pin). I read that from March 2018 it is mandatory to have at least one in each socket point. Wholesalers are not really carrying them and clients have 'not taking the news well'.
    I sent a mail out to all clients that the new socket is coming into effect with new installations. The general response was "why do I want that crap". Are all you guys using them now? In terms of C.O.C.'s on new installs? Some clients REALLY don't want them.

  2. #2
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,236
    Thanks
    34
    Thanked 304 Times in 258 Posts
    Hi

    The regulation (Sans 10142 Ed2 ) has been out since March 2017 warning us that it would take effect from Jan 2018 - From January you cannot sign a COC on new installations unless the socket outlet point complies.
    Any COC for a new installation that was issued after Jan 2018 and did not have a "euro" socket ( SANS164-2) installed at every socket outlet point is invalid - You could be held liable to return and correct the installation at your own cost.
    At the moment there is no option but to install.


    SANS 10142-1 ED 2 - pg 177 - 6.15.1.1.1 c - effective from January 2018 all socket-outlet points for new electrical installations shall include at least one socket-outlet complying with the dimensions of SANS 164-2.Socket-outlets points may also include socket-outlets complying with the dimensions of SANS 164-1.

  3. #3
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,648
    Thanks
    3,304
    Thanked 2,676 Times in 2,257 Posts
    Blog Entries
    12
    Quote Originally Posted by GCE View Post
    Any COC for a new installation that was issued after Jan 2018 and did not have a "euro" socket ( SANS164-2) installed at every socket outlet point is invalid
    Hi Graham,

    Isn't this influenced by commencement date of the project? Pretty rough if the project started a year ago...

  4. #4
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,236
    Thanks
    34
    Thanked 304 Times in 258 Posts
    Hi Dave

    Yes and No answer but valid point - Page 3 of the code refers to the signing date of the contract - If the contract was signed before the publication date of March 2017 ( Date mentioned in the Foreward of the code) then you can continue with the old code
    Any contract signed after March 2017 would need to comply with the new socket requirement.The code gave us 9 months warning to assist in a bit of flexibility.

    I would not agree with anybody saying that my contract was signed in November with a due date of Febuary and therefore I can install according to the old code.

    We went through the argument in November with a tender that was put out in September and did not allow for the new socket requirement.When we were awarded the contract in November we pointed out the requirement and used it to our advantage.
    We also had a contract signed in April and due for completion in December which ran overtime and was finally finished in Feb 2018 - That was a bit of a grey area and took a bit of dancing to get around.

  5. #5
    Silver Member
    Join Date
    Mar 2008
    Posts
    352
    Thanks
    5
    Thanked 50 Times in 43 Posts
    I knew it was the new standard. Its just-
    1. Its just not going to work in some installations.
    2. The client DOES NOT want it.
    And finally, all wholesalers are still selling normally double sockets. If its an addition to an existing do they all have to have the new style socket.
    Can it still be signed of in terms if C.O.C.. The client needs a normal double socket. A normal socket and a new style won't work for the application? Or if the client requests old style sockets - then what?

  6. Thanks given for this post:

    ACEsterhuizen (26-Feb-19)

  7. #6
    Silver Member
    Join Date
    Mar 2008
    Posts
    352
    Thanks
    5
    Thanked 50 Times in 43 Posts
    In cab strut now. The cradles and cover plates don't have capacity for a new and old style..... They are not aware....

  8. #7
    Silver Member
    Join Date
    Mar 2008
    Posts
    352
    Thanks
    5
    Thanked 50 Times in 43 Posts
    And builders warehouse/makro/mica. Still all selling old style.

  9. #8
    Junior Member
    Join Date
    Jul 2010
    Location
    P.E.
    Posts
    21
    Thanks
    3
    Thanked 0 Times in 0 Posts
    What do we do when installing new Orange Industrial Socket Outlets in Factories.

    Also installing a lot of Power skirting soon with 2x4 plugs in them.

  10. #9
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,236
    Thanks
    34
    Thanked 304 Times in 258 Posts
    Hi

    Will try answer the questions above as I see them

    We , as Electrical Contractors, seem to spend to much time worrying about what the client wants and start stuttering when he tells us NO - At the end of the day we are legally responsible for the COC and that client will be extremely quick to turn around at a later stage when something goes wrong , or insurance does not pay out. Insurance look for any reason not to pay and are using professionals , and AIA's , to inspect and verify electrical COC's.
    The alarm installers, car manufactures , insurance companies, banks etc will not budge from what they say is the law
    Trying telling the banks you are not going to comply with FICA , you just will have to do without a bank account.
    We as electrical contractors should be all in this together as we all operate under the same laws.

    The regulations as they stand say you must have a euro socket at every outlet point - Then I don't see how you can do a new installation without sticking to the regulations, as the COC cannot be valid if the installation does not comply.

    If we have a look at the definition of Installation work in the OHSA , which is what gives SANS 10142 teeth , it defines it as - the installation, extension, modification or repair of an electrical installation.
    I see the replacement of a faulty socket outlet as "repair of an electrical installation " and would therefore need to install a euro

    What the suppliers want to hold as stock and try and sell is not our problem - We need to install sockets with euro's and so the supplier must supply me with what I request - I am the one signing the COC and taking responsibility not them.If everybody was working according to the regulations then they would have a serious amount of dead stock.Some of our suppliers have already changed there stock holdings with regards to socket outlets.
    The manufactures are all well aware of the changes as some of them had an integral part in making those changes .

    Industrial sockets are a problem at the moment and the only way round is to install a socket and extension box.

    Power skirt - We install 1 euro for every normal 16 amp socket - There are the module power skirt covers and sockets available for most power skirts and socket manufacturers.If your supplier has not kept up with the times then it is still not a valid reason to sign off an installation that does not comply - Rather change suppliers

    Certain socket manufacturers have module type 4x4 sockets available where you can still put 2 normal round pin sockets and 2 euro's into a 4x4 box - A socket outlet does not need to be switched.

    There are Euro rewireable plug tops available which can be fitted to appliances - The plug tops should take care of most clients objections.

  11. Thanks given for this post:

    Trevor Varner (26-Aug-20)

  12. #10
    Silver Member
    Join Date
    Mar 2008
    Posts
    352
    Thanks
    5
    Thanked 50 Times in 43 Posts
    I spike to the ECA this morning (recorded the call and everything). Their guy said- If its a new install from the ground up then yes 100% you MUST have the Euro Socket. If its an addition to an existing then its a bit if tricky area. If the quote/job was agreed before January its another thing. As clear as I read the regs I can't see the change over being being smooth. I'm now going to tell my clients that there is an additional charge for every socket point I have quoted on.

Page 1 of 4 123 ... LastLast

Similar Threads

  1. Normal sockets on the floor?
    By skatingsparks in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 26-Mar-18, 11:23 AM
  2. SA to get new electrical sockets, plugs
    By adrianh in forum Technology Forum
    Replies: 19
    Last Post: 10-Mar-17, 04:52 AM
  3. Unswitch sockets ok?
    By skatingsparks in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 28-Nov-16, 12:34 PM
  4. crabtree plug sockets
    By murdock in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 05-Aug-12, 10:10 PM
  5. atx sockets
    By bergie in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 10-Apr-12, 12:56 AM

Tags for this Thread

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •