    Hi to you all, how do i get pipes from the DB to the end of the pipe( in powerskirting) open? Its not old pipes (6-10 months). The fishtape goes up to 75% into the pipe, but then got stuck. There was no previous wires in the pipe.

  2. #2
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,236
    Thanks
    34
    Thanked 304 Times in 258 Posts
    Hi

    Have you tried from the other end - Does it get stuck at about the same place ? Assuming it is 20mm or 25mm

    Do you have a wire wizard that you can pump air down the pipe and see if it will dislodge or at least get air out the other side - If you do not get air out then the chances are that a coupling came loose during the concrete pour

    Other method is to stick a hosepipe on and try flush with water -

    If there is a bit of cement in the pipe , leave pool acid in the pipe overnight and try flush the next morning , obviously acid comes with it's own set of problems

  3. #3
    New Member
    Join Date
    Oct 2017
    Location
    Kimberley
    Posts
    8
    Thanks
    3
    Thanked 0 Times in 0 Posts
    Thanks, i'll try to get a compressor and pump air through the pipes. I think it is small pieces of cement that got stuck

Similar Threads

  1. [Question] Can plumbing pipes (copper etc) be installed next to and behind my DB & across my conduit?
    By ACEsterhuizen in forum Electrical Contracting Industry Forum
    Replies: 6
    Last Post: 22-Jan-16, 09:15 AM
  2. 2 zone under floor heating thermostat
    By skatingsparks in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 29-Jul-14, 10:12 PM
  3. Bats or mice in my walls and finished 3rd floor?
    By victorbron5 in forum Pest Control Industry Forum
    Replies: 16
    Last Post: 18-Sep-13, 01:26 PM
  4. no need to earth metal downlights if they are "out of arms reach from the floor l"???
    By billybob2475 in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 07-Jun-11, 08:47 PM
  5. Floor-crossing season.
    By Dave A in forum General Chat Forum
    Replies: 22
    Last Post: 24-Nov-08, 09:33 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •