    DB wiring and CoC

    Greetings,

    I have an old (well, 21/22 year old) townhouse with three-phase electricity supply from the City of Joburg. All the wires in the DB board are solid copper conductors. For some reason, however, when the house was built in 1996 ,the builders/electricians only used red PVC insulated wires.... No other colours! My electrician tells me that he cannot issue a CoC due to the color-coding issue and what the "electrical code" says (he does say that the wiring itself is properly done).

    Are there any contrary views? Do I have to shell out a few thousand precious Rands for the re-wiring of the DB?

  2. #2
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,236
    Thanks
    34
    Thanked 304 Times in 258 Posts
    Hi

    reading between the lines and would not want to say anything until I saw a picture of the DB wiring .
    Could you possibly post a photo of the DB internal wiring

  3. #3
    Full Member
    Join Date
    Jun 2016
    Location
    Port Elizabeth
    Posts
    28
    Thanks
    0
    Thanked 1 Time in 1 Post
    Good day,
    I copied this out of SANS 10142-1 2017
    6.3.3.2 The means of identification for an a.c. circuit may be by colours or
    by numbers, as follows:
    a) where colours are used
    1) a neutral conductor shall be identified by black only,
    2) an earth continuity conductor shall be identified by the bi-colour
    green/yellow only, or by being bare. Green/yellow insulated
    conductors shall NOT be used as live conductors under any
    circumstances,
    3) a phase conductor shall be identified by a colour other than
    green/yellow, green or black, and
    NOTE Welding cable manufactured to SANS 1576 should not be used in
    circuits above 100 V.
    4) the colours may be applied at the ends of the conductor (of a
    multicore cable) by means of durable colour marking (e.g. insulating
    sleeves or by electrical insulating tape wound more than once around
    the conductor), and
    b) where numbers are used, "0" shall indicate the neutral conductor.
    NOTE Where the purpose or the function of a conductor is apparent, marking is
    not required.

    From what is printed in the standard, it does not state that each phase conductor should be a different colour.
    I could be wrong.

  4. #4
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    Ask the electrician for the regulation he's enforcing. Even if there is a reg, rewiring certainly isn't necessary. The phase colour can be indicated by a band of tape or heat shrink sleeve or even coloured cable straps at the point where the wire terminates.
    _______________________________________________

    _______________________________________________

  5. #5
    New Member
    Join Date
    Feb 2018
    Location
    Johannesburg
    Posts
    3
    Thanks
    0
    Thanked 0 Times in 0 Posts

    BD Board pics

    Quote Originally Posted by GCE View Post
    Hi

    reading between the lines and would not want to say anything until I saw a picture of the DB wiring .
    Could you possibly post a photo of the DB internal wiring
    Pics attached.
    Attached Thumbnails Attached Thumbnails Click image for larger version. 

Name:	IMG_0896.jpg 
Views:	345 
Size:	58.6 KB 
ID:	7012   Click image for larger version. 

Name:	IMG_0897.jpg 
Views:	360 
Size:	48.1 KB 
ID:	7013   Click image for larger version. 

Name:	IMG_0898.jpg 
Views:	349 
Size:	58.8 KB 
ID:	7014  

    Click image for larger version. 

Name:	IMG_0899.jpg 
Views:	329 
Size:	58.3 KB 
ID:	7015  

  6. #6
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,236
    Thanks
    34
    Thanked 304 Times in 258 Posts
    Hi

    Dont see the need for a rewire
    The regulation posted above by Hotspot should sort out any argument - All the live wires are red which is not an issue .

    Without going into details there are a couple of things to be sorted out on the DB , but complete rewire of the installation is a no.

  7. #7
    New Member
    Join Date
    Feb 2018
    Location
    Johannesburg
    Posts
    3
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Thanks all... Much appreciated.

  8. #8
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    Looks better than a lot of DB installation i get to see on a daily basis.

    I think you need to get a second opinion.

Similar Threads

  1. [Question] Wiring under thatch
    By camrad in forum Electrical Contracting Industry Forum
    Replies: 9
    Last Post: 07-Sep-17, 05:32 AM
  2. Old wiring still legal?
    By joshthejew in forum Electrical Contracting Industry Forum
    Replies: 6
    Last Post: 26-Sep-16, 08:44 AM
  3. Hobby wiring: Wiring requirements for a DCC railway layout
    By icrob in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 23-Jul-16, 05:29 PM
  4. wiring an inverter to DB
    By cje in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 11-Jul-15, 09:09 AM
  5. [Opinion] What type of wiring?
    By 123 in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 22-Apr-10, 11:32 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •