    5A Unswitched Circuits

    Hi Guys

    I need advise on light circuits wired with unswitched 5A round plugs.

    A light circuit are wired with 5A unswitched plugs . Lets say 5 recess florescent light fittings to be plug in.
    Ho do i record it on the coc? What if i have a fan also plugged in on the circuit with a 5a unswitched plug?
    Is it a mixed circuit ,yes or no ? I know when something plug in ,it is regarded as not part of the installation ?

    Appreciate your advise.

    Jaboel

  2. #2
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,236
    Thanks
    34
    Thanked 304 Times in 258 Posts
    Hi
    Would mark it on the coc as a light point - only one fitting per socket - Fan may not be plugged into a 5 amp socket.
    If something is plugged in and the cord is clipped to the skirting , or through a wall , or longer than 3m , then it is part of the fixed installation ( 6.16.1.9 ed 2 )
    I have pasted a discussion below that I had previously -



    Question was – Can you connect a bathroom type fan to the light fitting in a bathroom –

    If we look at 6.16.1.3. – It refers to the fan incorporated into a luminaries – in this case you can protect by earth leakage and ignore the isolator

    Then back to 6.16.1.2 – Every fixed appliance shall be supplied through a switch disconnector – The fan being referred to in the question was a “stand alone type fan” and therefore would need an isolator ( ELU will not be allowed )

    6.14.1.4 – A lighting circuit may use a socket complying with SANS 164-3 (b) supplies one luminaries only –* I read this as saying that only luminaries can be fed from a 6 amp socket and not fans .

    6.16.4 – Heaters appliances for heating and cooling – note 3 includes extraction and ventilation fans – refers to dedicated circuits over 16Amp – so would assume that small extraction fans could go onto a mix loaded circuit as long as it has an isolator
    6.16.5.1.4 – basically states that you may not use a double pole c/breaker to act as the isolator in the D/board* for the extract fan
    6.15.4.2 – allows for mixed loading of non dedicated single phase circuits not rated above 20 amps and may feed luminaries and fixed appliances*


    The answer – Yes you may connect the fan to the luminaries circuit as long it is fed by an isolator , taking into account 6.16.5.1.4,* and that the circuit is labelled as mixed loaded in the DB

  3. #3
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,236
    Thanks
    34
    Thanked 304 Times in 258 Posts
    Further to the above post from 2017

    For info and to keep up with changes

    In previous editions of SANS 10142-1 you were not allowed to use a 5 Amp socket ( SANS 164-3) outlet for a "bathroom fan "

    The latest Ed 3 of SANS 10142-1 now finally allows it , reg pasted below

    6.16.4.3 Extraction fans
    Where an extraction fan supply is switched with a luminaire, it shall be
    connected to the switched portion of the light circuit, provided that the fan
    circuit is connected by means of a SANS 164-3 or SANS 164-2-1 or
    SANS 164-2-2 socket-outlet or a switch disconnector

  4. Thanks given for this post:

    Dave A (08-Aug-21)

Similar Threads

  1. Dedicated plug circuits, what is allowed to be supplied by a non earth leakage protected socket?
    By hartdev@hotmail.com in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 19-May-17, 06:52 AM
  2. Underfloor heating circuits
    By kosmonooit in forum Electrical Contracting Industry Forum
    Replies: 11
    Last Post: 26-Oct-16, 02:52 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •