    Cleat wiring in Electrical installation

    Hi all! I need a bit of help. is the old wiring that is held by porcelain clips in the ceiling still allowed? Where GP or house wire is visible. Some houses the gp wires is insulated by normal PVC, some houses it's that insulation which is fabric (sorry don't know the name)?

    Thanks
    Simps

  2. #2
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,236
    Thanks
    34
    Thanked 304 Times in 258 Posts
    The old wiring you refer to is VIR wiring ( vulcanised India Rubber ) and was used extensively on the cleat system.
    When the wiring was manufactured it had a life span of 25 years - As far as I am aware they stopped manufacturing almost 40 years ago - If you looked through Fundamental requirements note 2 pg 62 in SANS 10142-1 "manufacturers instructions may contain more stringent requirements " - I would say the VIR wiring is not allowed and would not sign a COC

    With regards to open wiring , there is a section in SANS 10142-1 ED2 - 6.4.5 pg 139 - that appears to allow it but not recommended - Have no idea why they still allow open wiring

  3. Thank given for this post:

    AndyD (06-Dec-17), shnzimande@hotmail.com (31-Dec-17)

  4. #3
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    Just be careful, from experience VIR / cotton wrapped wiring tends to be fine and test well until it's disturbed. Even gently tipping a socket or switch forward to visually inspect can result in the rubber insulation disintegrating.
    I'm with GCE, anywhere I found VIR still in service I'd recommend replacement / rewiring as a matter of course and regardless of how it tested.
    _______________________________________________

    _______________________________________________

  5. #4
    New Member shnzimande@hotmail.com's Avatar
    Join Date
    May 2017
    Location
    Benoni
    Posts
    6
    Thanks
    3
    Thanked 0 Times in 0 Posts
    Thank you so much for the information.

  6. #5
    Gold Member Sparks's Avatar
    Join Date
    Dec 2009
    Location
    Port Elizabeth
    Posts
    890
    Thanks
    20
    Thanked 127 Times in 96 Posts
    Should VIR wiring be accepted it must comply with the regulations as at the time of installation. The installation must be unchanged, no joints to extend/ add points. The wires must not be sagging(almost impossible by now), it must clear the roof by .75m(if I recall correctly) and wires are not allowed to touch each other. There must also be slack with a curve where it enters the droppers which must all be earthed. Insulation readings tend to be good with the exception of lighting circuits. As Andy said, best is to replace it. I have not accepted one in years.

  7. Thank given for this post:

    ACEsterhuizen (13-Dec-17), shnzimande@hotmail.com (31-Dec-17)

Similar Threads

  1. Compliance of electrical wiring in ceiling space
    By mygoggie in forum Electrical Contracting Industry Forum
    Replies: 14
    Last Post: 03-Jul-19, 09:57 AM
  2. [Opinion] 3 phase electrical distribution board wiring
    By Stephenvr in forum Electrical Contracting Industry Forum
    Replies: 9
    Last Post: 26-Nov-17, 07:02 PM
  3. [Article] New electrical installation regulations
    By QUINN in forum Electrical Contracting Industry Forum
    Replies: 12
    Last Post: 11-Jun-14, 03:01 PM
  4. Who may work on an electrical installation?
    By douw in forum Electrical Contracting Industry Forum
    Replies: 37