    Cleat wiring in Electrical installation

    Hi all! I need a bit of help. is the old wiring that is held by porcelain clips in the ceiling still allowed? Where GP or house wire is visible. Some houses the gp wires is insulated by normal PVC, some houses it's that insulation which is fabric (sorry don't know the name)?

    Thanks
    Simps

  2. #2
    Junior Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    12
    Thanks
    0
    Thanked 2 Times in 2 Posts
    The old wiring you refer to is VIR wiring ( vulcanised India Rubber ) and was used extensively on the cleat system.
    When the wiring was manufactured it had a life span of 25 years - As far as I am aware they stopped manufacturing almost 40 years ago - If you looked through Fundamental requirements note 2 pg 62 in SANS 10142-1 "manufacturers instructions may contain more stringent requirements " - I would say the VIR wiring is not allowed and would not sign a COC

    With regards to open wiring , there is a section in SANS 10142-1 ED2 - 6.4.5 pg 139 - that appears to allow it but not recommended - Have no idea why they still allow open wiring

  3. Thanks given for this post:

    AndyD (06-Dec-17)

  4. #3
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,403
    Thanks
    513
    Thanked 854 Times in 687 Posts
    Just be careful, from experience VIR / cotton wrapped wiring tends to be fine and test well until it's disturbed. Even gently tipping a socket or switch forward to visually inspect can result in the rubber insulation disintegrating.
    I'm with GCE, anywhere I found VIR still in service I'd recommend replacement / rewiring as a matter of course and regardless of how it tested.
    _______________________________________________
    I am special and so is Vanash.
    _______________________________________________

  5. #4
    New Member
    Join Date
    May 2017
    Location
    Benoni
    Posts
    6
    Thanks
    1
    Thanked 0 Times in 0 Posts
    Thank you so much for the information.

  6. #5
    Gold Member Sparks's Avatar
    Join Date
    Dec 2009
    Location
    Port Elizabeth
    Posts
    826
    Thanks
    15
    Thanked 112 Times in 90 Posts
    Should VIR wiring be accepted it must comply with the regulations as at the time of installation. The installation must be unchanged, no joints to extend/ add points. The wires must not be sagging(almost impossible by now), it must clear the roof by .75m(if I recall correctly) and wires are not allowed to touch each other. There must also be slack with a curve where it enters the droppers which must all be earthed. Insulation readings tend to be good with the exception of lighting circuits. As Andy said, best is to replace it. I have not accepted one in years.

  7. Thanks given for this post:

    ACEsterhuizen (13-Dec-17)

Similar Threads

  1. [Opinion] 3 phase electrical distribution board wiring
    By Stephenvr in forum Electrical Contracting Industry Forum
    Replies: 9
    Last Post: 26-Nov-17, 07:02 PM
  2. Compliance of electrical wiring in ceiling space
    By mygoggie in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 29-Apr-17, 12:55 PM
  3. [Article] New electrical installation regulations
    By QUINN in forum Electrical Contracting Industry Forum
    Replies: 12
    Last Post: 11-Jun-14, 03:01 PM
  4. Who may work on an electrical installation?
    By douw in forum Electrical Contracting Industry Forum
    Replies: 37
    Last Post: 16-Apr-10, 11:57 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •