    Updating and making safe an electrical install from 1973

    Hi,

    I have bought a house built in 1973. Came of course with a Electrical CoC but the state of the DB does not fill me with happiness and confidence.

    I’d like to get it right.

    Here’s a picture:

    Click image for larger version. 

Name:	4579DBB3-4559-411D-BFFC-09FBD3F42F1B.jpg 
Views:	444 
Size:	86.5 KB 
ID:	6921

    I’m looking for opinion - myself I’d like to replace all the old breakers with new 13mm units.

    1. Separate main switch and breaker to a combined dual-pole breaker
    2. Two RCDs - one for lights, one for everything else? (will I be sorry putting everything on earth leakage?)
    3. 4 light circuits (10A)
    4. 1 send to the pool db (15A)
    5. 3 plug circuits (20A)


    Or something like that.

    But I’m looking for advice before discussing with my electrician.

    Thanks,
    Elbow

  2. #2
    Gold Member Sparks's Avatar
    Join Date
    Dec 2009
    Location
    Port Elizabeth
    Posts
    890
    Thanks
    20
    Thanked 127 Times in 96 Posts
    When did you buy the house? By virtue of the fact that none of the Heineman breakers have ratings, they should have been replaced if certified recently.

  3. #3
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    I particularly like that technique of saving the price of a neutral bar by ramming multiple neutral wires directly into the bottom of the earth leakage breaker.

    I'm not sure why you'd require 4x lighting circuits unless the house is enormous. If you're planning on putting everything on earth leakage then be sure to IR test all the circuits first, it can save a lot of misery.

    TBH I'd strongly suggest you get a good electrician to help you out. Some of those circuits don't have a CPC (earth wire), they are using the steel conduit as the earth. Those circuits particularly need testing and visually inspecting to ensure they're safe and if any changes are done to the installation you really should rewired with an earth. Also the earth bar doesn't appear to have a main earth wire from the supply so it's highly likely the main earth is via the steel conduit of the incoming supply and via the steel chassis of the DB. Again this arrangement needs testing and inspecting before proceeding with any other work.

    Please get a competent sparky involved, it only takes some corrosion in the wrong conduit to cause a grave safety hazard.
    _______________________________________________

    _______________________________________________

Similar Threads

  1. Inverter Install Compliance
    By deejaypsy in forum Electrical Contracting Industry Forum
    Replies: 43
    Last Post: 06-Mar-23, 07:14 AM
  2. How to Install Old Wordpress
    By nurr in forum Technology Forum
    Replies: 3
    Last Post: 11-Sep-20, 03:32 PM
  3. EasyFile error message after updating
    By Daneel1983 in forum Tax Forum
    Replies: 4
    Last Post: 03-May-17, 10:12 AM
  4. Problems updating e@syfile
    By Scottc in forum Technology Forum
    Replies: 4
    Last Post: 09-Dec-11, 08:13 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •