    Airdac CAble in roof spaces

    Hi guys

    Can anybody help me locate where in the new regulation (SANS 10142-1 Ed 2) it refers to the fact that the standard 16mm Airdac cable is not allowed in a roof space due to the fact that it is not ("Fire proof")
    I cannot find my copies of SANS 1507 or 529 (not sure if its even in there or if that is where the answer will be.)
    My issue is that the municipality installs this as the main supply to properties and obviously clients will be thinking im out to make a quick buck when i tell them this is illegal.

    Thanks for the help and swear me softly please!

  2. #2
    Bronze Member
    Join Date
    Mar 2012
    Location
    Account_Deleted
    Posts
    165
    Thanks
    122
    Thanked 23 Times in 18 Posts
    Your issue with the municipality (hereafter referred to as the "supplier", is this:

    (been there done that got the keyring)

    Page 38: (Edition 2017)

    3.33
    electrical installation - (what a CoC certifies : "an electrical installation as defined")

    machinery, in or on any premises, that is used for the transmission of
    electrical energy from a point of control (see 3.56) to a point of
    consumption
    (see 3.55) anywhere on the premises, including any article
    that forms part of such an installation, irrespective of whether or not it is part
    of the electrical circuit, but excluding


    a) any machinery of the supplier that is related to the supply of electricity on
    the premises,
    b) any machinery that is used for the transmission of electricity of which the
    voltage does not exceed 50 V, where such electricity is not derived from
    the main supply of a supplier, and
    c) any machinery that transmits electrical energy in telecommunication,
    television or radio circuits

  3. #3
    New Member
    Join Date
    Jul 2013
    Location
    Durban
    Posts
    7
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Thanks ACE
    Is there however any reference that i can make in regards to the actual cable as clients tend to rely more on the writen word than my opinion?

  4. #4
    Gold Member Sparks's Avatar
    Join Date
    Dec 2009
    Location
    Port Elizabeth
    Posts
    890
    Thanks
    20
    Thanked 127 Times in 96 Posts
    The municipal supply cable is not covered by the COC when you certify the installation.
    a) any machinery of the supplier that is related to the supply of electricity on
    the premises.

  5. Thanks given for this post:

    ACEsterhuizen (27-Jun-17)

  6. #5
    Email problem
    Join Date
    Sep 2010
    Location
    cape town
    Posts
    308
    Thanks
    3
    Thanked 43 Times in 37 Posts
    whats the story with it being " fireproof" ? does it mean "flame retardant" and wont burn if there is a fire? or "flameproof" and cant cause a fire?

Similar Threads

  1. roof sheeting
    By Razinatjie in forum General Chat Forum
    Replies: 3
    Last Post: 18-Jul-13, 08:32 AM
  2. Electrical Fire in my roof
    By daveob in forum Electrical Contracting Industry Forum
    Replies: 4
    Last Post: 21-Feb-11, 02:01 PM
  3. [Article] Exe cable glands for braided cable
    By Master Electrician in forum Electrical Contracting Industry Forum
    Replies: 0
    Last Post: 26-Aug-10, 02:47 PM
  4. [Question] Ducting in a roof
    By Jacques#1 in forum Electrical Contracting Industry Forum
    Replies: 19
    Last Post: 22-Jul-10, 09:32 AM
  5. Only 4 Spaces Left
    By JMGROUP in forum General Business Forum
    Replies: 2
    Last Post: 10-Jun-08, 01:28 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •