    Earth leakage unit trips at 15mA

    A ramp test shows an earth leakage unit trips at 15 milliAmps.

    Do you replace it?

  2. #2
    Full Member
    Join Date
    Apr 2016
    Location
    South Africa
    Posts
    75
    Thanks
    34
    Thanked 1 Time in 1 Post
    These are the things I wrestle with as an installation electrician . As far as I know the tripping value of a earth leakage unit must be 30mA (0 to 50 % of 30mA)that is 15 to 30 mA. A value on a earth leakage tester is 15 mA. So from that point of view it can legally pass .Being border line the earth leakage could be deteriorating .Due to nature and reason for earth leakage protection it may be better to replace.Is a ramp test the. same as a earth leakage test.

    Sent from my HUAWEI VNS-L31 using Tapatalk

  3. #3
    Full Member
    Join Date
    Apr 2016
    Location
    South Africa
    Posts
    75
    Thanks
    34
    Thanked 1 Time in 1 Post
    If a earth leakage trips at 15 mA this could /will lead to nuisance tripping.

    Sent from my HUAWEI VNS-L31 using Tapatalk

  4. #4
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    What was the exact test procedure Dave? Was it tested several times with consistent results? What was the tripping time and what time at 180degrees? Was all wiring on the outgoing side disconnected?

    Is the earth leakage covering the entire installation or just a few of the circuits?

    I often come across earth leakage units that trip outside the required tolerances until they've been operated a couple of times either by tripping during testing or by operating the test button. Usually if they just fail the initial test then pass consistently after that I don't replace them. I wouldn't replace a unit that was tripping at 15mA unless there were specific reasons it might be a nuisance
    _______________________________________________

    _______________________________________________

  5. Thanks given for this post:

    Gtfast (31-Mar-17)

  6. #5
    Full Member
    Join Date
    Apr 2016
    Location
    South Africa
    Posts
    75
    Thanks
    34
    Thanked 1 Time in 1 Post
    A bit late.
    Reg 8.7.12 says it must not trip at 50 percent of rated tripping current which I understand to be 15mA.

    Sent from my HUAWEI VNS-L31 using Tapatalk

  7. Thanks given for this post:

    Dave A (12-May-17)

  8. #6
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,648
    Thanks
    3,304
    Thanked 2,676 Times in 2,257 Posts
    Blog Entries
    12
    Quote Originally Posted by Gtfast View Post
    A bit late.
    Reg 8.7.12 says it must not trip at 50 percent of rated tripping current which I understand to be 15mA.
    Better late than never. Thanks for that.

    Just to note your reference applies to edition 1.8.

    The new reference is 8.6.12 in edition 2.

  9. #7
    Full Member
    Join Date
    Apr 2016
    Location
    South Africa
    Posts
    75
    Thanks
    34
    Thanked 1 Time in 1 Post
    Thanks

    Sent from my HUAWEI VNS-L31 using Tapatalk

Similar Threads

  1. Earth Leakage Unit Question
    By Slow Blow in forum Electrical Contracting Industry Forum
    Replies: 24
    Last Post: 26-Jun-16, 10:50 PM
  2. Earth leakage trips then stops.
    By Boeriemore in forum Electrical Contracting Industry Forum
    Replies: 12
    Last Post: 21-Dec-13, 04:08 PM
  3. Earth leakage trips when it's raining - pool pump unit the cause.
    By Boeriemore in forum Electrical Contracting Industry Forum
    Replies: 10
    Last Post: 29-Nov-13, 04:25 PM
  4. Earth leakage trips at night??
    By Jongseun in forum Electrical Contracting Industry Forum
    Replies: 18
    Last Post: 18-Jun-12, 10:47 PM
  5. earth leakage unit failure
    By murdock in forum Electrical Contracting Industry Forum
    Replies: 11
    Last Post: 23-Feb-12, 08:37 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •