    Fixed appliances

    What is the regulations saying with regards to three phase and single phase cooking appliances used in take away stores for example that is feed from a welding socket? The socket can also be classified as an isolator cause it serves the same perpose, but should it be on earth leakage or not? A fixed alliance don't need earth leakage protection cause its on an isolator but in this case its equipment thst s on wheels that can be moved for cleaning purposes due to the oil etc. I struggle to come to a solid point regarding this as there's so many points that almost sounds contradictory in sans 10142:1. And some equipment works on two phases and neutral but I haven't seen a 2 phase c\b except for live and neutral 2 pole circuit breakers and then the normal 3 pole circuit breakers. What's your opinion about this and issuing a coc for this kind of installation?

  2. #2
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,648
    Thanks
    3,304
    Thanked 2,676 Times in 2,257 Posts
    Blog Entries
    12
    When it comes to socket-outlets, section 6.15 must be taken into account.
    6.15.1.2.4 contains this -
    NOTE 1 Dedicated socket-outlets are the only socket-outlets that need not be protected by earth leakage.
    Then 6.15.1.2.6 contains this -
    NOTE 1 Earth leakage protection is not required for the stove circuit when a stove coupler is used.
    The use of the term "stove coupler" may cause some confusion (as it did during the interview of one of the candidates for a technical advisor post of the ECA(SA) last week), so for clarity -
    6.15.1.2.5 specifies -
    A stove coupler shall comply with the requirements of SANS 60309-1 and shall be of dimensions as given in SANS 337.

Similar Threads

  1. Isolators for Fixed Appliances
    By BlueArc in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 03-Feb-17, 08:03 AM
  2. Kitchen appliances - recommendations?
    By Basment Dweller in forum General Business Forum
    Replies: 28
    Last Post: 02-Oct-14, 06:10 PM
  3. 110VAC 60Hz Appliances from USA
    By douw in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 30-Jan-13, 05:55 PM
  4. gas appliances
    By murdock in forum General Chat Forum
    Replies: 17
    Last Post: 28-Jul-11, 08:28 AM
  5. bathrooms and fixed appliances
    By murdock in forum Electrical Contracting Industry Forum
    Replies: 12
    Last Post: 27-Jun-11, 07:03 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •