    Cooler/freezer room

    Good day all
    I have a question regarding cooler room in a butchery.
    It is wired with a 4mm cable and has a 30amp mcb in db. Should it have a switch-disconector also or is it fine as is? Its protected also by th elcb .

    Thanx

  2. #2
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    The cold room would be classed as a fixed appliance so I'd say it should have an isolator switch at the condensing unit unless the MCB in the DB is close enough and qualifies.
    _______________________________________________

    _______________________________________________

  3. #3
    Full Member
    Join Date
    Sep 2015
    Location
    port elizabeth
    Posts
    26
    Thanks
    0
    Thanked 1 Time in 1 Post
    This butchery has also a 3phase cold room and it is not protected by a ELCB. The client has spoken to his friend in JHB that is a MIE and he said it does not need to be protected by a ELCB. Is this true? I just need to confirm this,rather safe than sorry. Thanx for your input Andy

  4. #4
    Email problem
    Join Date
    Sep 2010
    Location
    cape town
    Posts
    308
    Thanks
    3
    Thanked 43 Times in 37 Posts
    it does not have to be protected by earth leakage relay. if it was plugged in to a socket outlet then it would need to be on earth leakage relay.

  5. Thanks given for this post:

    mikilianis (27-Dec-16)

Similar Threads

  1. Safe room door
    By ians in forum General Chat Forum
    Replies: 10
    Last Post: 21-May-13, 07:23 AM
  2. freezer room light fitting
    By ians in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 16-Jan-13, 09:21 PM
  3. Chat-room Propaganda.
    By tec0 in forum Technology Forum
    Replies: 6
    Last Post: 14-Jul-09, 10:54 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •