Results 1 to 8 of 8

Thread: Location of DB in old house

  1. #1
    Email problem
    Join Date
    Nov 2016
    Location
    Cape Town
    Posts
    5
    Thanks
    2
    Thanked 2 Times in 2 Posts

    Location of DB in old house

    We've recently sold an old house.
    When we purchased the house 25 years ago it had a FUSE BOX in the kitchen, near ceiling height.
    Subsequently rewired into a DB (with Earth leakage etc), but still 2.3m above floor level.

    Electrician issued a CoC after all relevant tests, BUT the new owner is challenging the legality of the DB, due to "health & safety reasons".
    New owner insists that the DB should be re-located down to a "safe height".

    Any firm regulations in this regard?

  2. #2
    Gold Member Sparks's Avatar
    Join Date
    Dec 2009
    Location
    Port Elizabeth
    Posts
    890
    Thanks
    20
    Thanked 127 Times in 96 Posts
    Regulations give minimum height only as far as I recall offhand. Being that you are in Cape Town though, I must ask: Is the DB above the stove? I have refused to certify that on a number of occasions.

  3. #3
    Bronze Member
    Join Date
    Mar 2012
    Location
    Account_Deleted
    Posts
    165
    Thanks
    122
    Thanked 23 Times in 18 Posts
    6.6.1.6

    Any point of a distribution board that has to be reached during
    normal operation shall not exceed a height of 2,2 m above floor (or walking)
    level.

    However, the board may be mounted higher if it can be disconnected
    from the supply by a switch-disconnector that is less than 2,2 m above floor
    level. (See also 5.2.8(b)).


    Unless a residential distribution board is housed in
    an enclosure and direct access cannot be obtained by an infant, no part of
    an indoor distribution board shall be less than 1,2 m above the floor level
    and no part of an outdoor distribution board shall be less than 0,2 m
    above the ground level.

    Is it 2.3 m from ANY POINT THAT HAS TO BE REACHED OF THE DB to ground walking level?

    If it is outside the 2.2m then install a "switch disconnector". If it is lower than 1.2m then put it in an "enclosure" that cannot be accessed by an infant..


    The "Switch Disconnector" does have to be in the same room. It can feed from the meter DB.

    3.36
    enclosure

    part that provides protection of equipment against certain external
    influences and, in any direction, protection against direct contact.

    3.79.2
    switch-disconnector

    switch that, in the open position, satisfies the isolating requirements
    specified for a disconnector
    NOTE A switch-disconnector was known as an "on-load isolator".

    5.2.8 Positioning and accessibility of electrical equipment

    b)
    it is readily accessible for installation, replacement, operation, testing,
    inspection, maintenance and repair (see 6.6.1.9 and 6.9.4 for the
    main switch). All parts of the installation shall be accessible without
    the need to enter any adjoining premises (for example, in an
    apartment building) * NOTE Common areas (such as passages and entrance halls) are not regarded as
    adjoining areas.
    Last edited by ACEsterhuizen; 28-Nov-16 at 07:49 PM. Reason: more info, spelling

  4. Thank given for this post:

    Dave A (28-Nov-16), iDon (29-Nov-16), Sparks (29-Nov-16)

  5. #4
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,924
    Thanks
    576
    Thanked 934 Times in 755 Posts
    CBI (I think it was CBI) used to have a kit that you could attach to the main breaker, it was like a hanging rod that clipped onto the levers that allowed it to be operated easily if the DB was mounted high.
    _______________________________________________

    _______________________________________________

  6. Thanks given for this post:

    iDon (29-Nov-16)

  7. #5
    Email problem
    Join Date
    Nov 2016
    Location
    Cape Town
    Posts
    5
    Thanks
    2
    Thanked 2 Times in 2 Posts
    Hi Sparks,
    Thanks for the quick response.
    The DB is NOT above the stove, or any electrical equipment.
    (We moved the stove isolator so that it was no longer above the stove prior to the issuance of the CoC)

    The DB is installed ABOVE a cupboard, on the wall, open to view, just below ceiling height.
    Directly BELOW the DB is the Prepayment meter (with a two pole isolator integral to the meter), inside a cupboard.
    The meter is 1.7m above ground level and easily visible / accessible once the cupboard door is opened.
    Thanks,
    Don

  8. Thanks given for this post:

    ACEsterhuizen (30-Nov-16)

  9. #6
    Email problem
    Join Date
    Nov 2016
    Location
    Cape Town
    Posts
    5
    Thanks
    2
    Thanked 2 Times in 2 Posts

    Thanks An Dee Dee!

    Sounds quite cool, Andy Dee.
    I'll look it up and see what is "currently" available!

  10. #7
    Email problem
    Join Date
    Nov 2016
    Location
    Cape Town
    Posts
    5
    Thanks
    2
    Thanked 2 Times in 2 Posts

    Monster big thanks to AC

    Wow, AC.
    Thanks for such a detailed and comprehensive response.
    Most useful.

    It would seem that, because the prepayment meter - complete with two pole isolator - is in the same room as the DB (directly below the DB and at a height of 1.7m), the installation can be considered Compliant.

    Most kind, all round.

  11. Thanks given for this post:

    ACEsterhuizen (30-Nov-16)

  12. #8
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,924
    Thanks
    576
    Thanked 934 Times in 755 Posts
    Quote Originally Posted by iDon View Post
    Sounds quite cool, Andy Dee.
    I'll look it up and see what is "currently" available!
    I think this is the modern day version, never used one so maybe check with their sales department.
    _______________________________________________

    _______________________________________________

Similar Threads

  1. Location Vs Timing
    By BusNavig8 in forum General Business Forum
    Replies: 2
    Last Post: 21-Oct-12, 11:47 AM
  2. [Question] Hazardous location Work experience
    By Jacechop in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 10-Apr-12, 05:00 PM
  3. What is deemed an explosive location?
    By Dave A in forum Electrical Contracting Industry Forum
    Replies: 13
    Last Post: 29-Sep-10, 08:43 AM

Tags for this Thread

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •