Results 1 to 4 of 4

Thread: 3 Phase Puzzle

  1. #1
    Full Member
    Join Date
    Jun 2012
    Location
    Plettenberg Bay
    Posts
    69
    Thanks
    1
    Thanked 17 Times in 13 Posts

    3 Phase Puzzle

    Hi there,
    I was wondering whether someone may be able to help me with an issue I have come across.
    I am testing an installation for compliance for a sale of property. It is a farm and is supplied by an Eskom 3 phase transformer.
    It is a 40A 3 phase supply.
    When I test from neutral to red I get 230V, neutral to yellow 230V and neutral to blue 230V.
    When I test from earth to red I get 230V, earth to yellow 230V and earth to blue 230V.
    When I test from red to yellow I get 412V, red to blue 411V. Now when I test from yellow to blue I get 0V!!
    How is this possible??
    I have tested right back at the Eskom box and I get this same result even at the meters in the Eskom box.
    I cannot test the top of the Eskom breakers as they are locked with tags.
    Someone please help shed some light on this.
    Luckily, at present, there is no 3 phase equipment installed on the premises, however the new owners may well install a 3 phase pump or something and then I would be sure that they would start having problems!
    Many thanks
    Simon
    We are not human beings undergoing a spiritual phase.....we are spiritual beings undergoing a human phase....

  2. #2
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,662
    Thanks
    3,307
    Thanked 2,676 Times in 2,258 Posts
    Blog Entries
    12
    Yellow and blue are supplied by the same phase.

  3. #3
    Full Member MullerR's Avatar
    Join Date
    Jan 2016
    Location
    Lady Grey
    Posts
    44
    Thanks
    3
    Thanked 6 Times in 5 Posts
    I agree with Dave. Try to get hold of Eskom to open their box (good luck with that). It could be that in the past the transformer gave problems with the one phase so they connected the two phases together. I had to do it once in an emergency situation,but changed the transformer a week after that.

  4. #4
    Full Member
    Join Date
    Jun 2012
    Location
    Plettenberg Bay
    Posts
    69
    Thanks
    1
    Thanked 17 Times in 13 Posts
    Quote Originally Posted by MullerR View Post
    I agree with Dave. Try to get hold of Eskom to open their box (good luck with that). It could be that in the past the transformer gave problems with the one phase so they connected the two phases together. I had to do it once in an emergency situation,but changed the transformer a week after that.
    Thanx guys.
    This was the only logical conclusion that I could come to as well. I stood on the ground under the transformer and looked up at it and it certainly looked like all 3 phases were separate at the transformer.
    They all had their own tappings off of the windings and nowhere were they even bridged across each other.
    This puzzled me, as if it is, and it must be, like you suggested, then either the transformer has shorted its windings inside the transformer, or it is bridged further down the line somewhere?!
    I will see if I can get onto Eskom today.
    I'll update once I resolve this one...
    Peace
    We are not human beings undergoing a spiritual phase.....we are spiritual beings undergoing a human phase....

Similar Threads

  1. 3 phase moor/2 phase supply
    By Leecatt in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 17-Jul-15, 01:24 AM
  2. Three phase to single phase generator advice needed
    By joshthejew in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 08-Apr-15, 10:12 PM
  3. Electronics Puzzle
    By daveob in forum General Chat Forum
    Replies: 0
    Last Post: 14-Apr-10, 08:12 PM
  4. [Question] Single phase and 3 phase testing course
    By skatingsparks in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 26-Feb-09, 09:14 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •