    Old wiring still legal?

    is this form of open wiring still legal if it was done before 1994? its so hard to believe that its still good.
    Click image for larger version. 

Name:	IMG_2879.jpg 
Views:	484 
Size:	40.0 KB 
ID:	6482

    Click image for larger version. 

Name:	IMG_2880.jpg 
Views:	529 
Size:	68.9 KB 
ID:	6483

    Click image for larger version. 

Name:	IMG_2881.jpg 
Views:	671 
Size:	74.1 KB 
ID:	6484

  2. #2
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,648
    Thanks
    3,304
    Thanked 2,676 Times in 2,257 Posts
    Blog Entries
    12
    See section 6.4.5 of SANS 10142-1
    It's not recommended, but you can still install it to this day if you're so inclined.

  3. #3
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    I'd test the earth impedance of all the circuits before getting involved in any further work on the installation. There's a few worrying things visible in the pictures, I don't see any CPC's of method of supplying the circuits with an earth. Also the points where the original wiring and newer circuits have been teed off look very suspect.
    _______________________________________________

    _______________________________________________

  4. #4
    Junior Member
    Join Date
    May 2014
    Location
    Mossel Bay
    Posts
    23
    Thanks
    1
    Thanked 1 Time in 1 Post
    thanks andy. haven't done the impedance test yet but there was earth on all the plug points. The DB was also using newish CBI cab's so you can't really tell if it was before or after 1994. Maybe that electrician was being a cheapskate

  5. #5
    Bronze Member
    Join Date
    Mar 2012
    Location
    Account_Deleted
    Posts
    165
    Thanks
    122
    Thanked 23 Times in 18 Posts
    Without diving in to deep, and not having done the inspection, it seems this open wiring breaks a few regulations: (just from visuals)



    6.4.5 Open wiring

    NOTE Open wiring consists of single-core insulated conductors that operate at not
    more than 250 V to earth; however, this is not a recommended installation method
    for new installations. Amdt 5

    6.4.5.1 Open wiring shall not be installed

    a) under thatched or wood-shingle roofs,
    b) in parts of a roof space where the working height is less than 750 mm,
    c) in roof spaces that are intended to be used (or are used) for storage,
    unless the wiring is suitably protected against mechanically damage,
    Amdt 5
    d) within 1 m of a trap door unless the wiring is suitably protected
    against mechanical damage, or Amdt 5
    e) where it will be in contact with flammable material.

    6.4.5.2 Each conductor of an open wiring system shall be visible where it
    is installed on, over, or next to beams that can be used for walking on, or
    it shall be suitably protected against mechanical damage. Amdt 5

    6.4.5.3 Conductors shall
    a) be fixed at intervals not exceeding 1,5 m to building elements such as
    walls, rafters or purlins, Amdt 5
    b) if there is no ceiling, be at least 3 m above floor level,
    c) Deleted by amendment No. 5.
    d) Deleted by amendment No. 5.
    e) Deleted by amendment No. 5.
    f) be supported within 600 mm of the point where they enter conduit or
    other building elements, and Amdt 5
    g) be fixed in such a way that the fixing method does not impair the
    conductor insulation
    . Amdt 5
    6.4.5.4 Where conductors enter a conduit, the conductors shall not be
    strained. Metal conduit shall project enough to allow a bush and an earth
    clip to be fitted
    . Amdt 1; amdt 5
    6.4.5.5 Where the current-carrying capacity of conductors is impaired by
    thermal insulating the appropriate correction factors shall be
    applied. Amdt 5

    (is wood flammable?)

    When the conditions are right, it seems to be.

  6. #6
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    I'm not sure of the date it might have been installed. Is the original wiring all PVC insulated or is there cotton insulated conductors as well? For me I think I'd probably recommend a rewire given that there are already numerous non-compliant issues with the existing installation, looking at the basic nature of the installation I think it would probably be the fastest and cheapest route to compliance all things considered.
    _______________________________________________

    _______________________________________________

  7. #7
    Email problem ThomasWinfrey's Avatar
    Join Date
    Sep 2016
    Location
    Toronto, ON
    Posts
    1
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Quote Originally Posted by Dave A View Post
    See section 6.4.5 of SANS 10142-1
    It's not recommended, but you can still install it to this day if you're so inclined.
    I agree with Dave.

Similar Threads

  1. [Question] Wiring under thatch
    By camrad in forum Electrical Contracting Industry Forum
    Replies: 9
    Last Post: 07-Sep-17, 05:32 AM
  2. Hobby wiring: Wiring requirements for a DCC railway layout
    By icrob in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 23-Jul-16, 05:29 PM
  3. wiring an inverter to DB
    By cje in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 11-Jul-15, 09:09 AM
  4. Statutory adjustment from an employee - legal or not legal?
    By peanuts in forum Labour Relations and Legislation Forum
    Replies: 1
    Last Post: 16-Feb-11, 12:12 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •