Thread: oosterzee box usage

  1. #1
    Full Member markthespark's Avatar
    Join Date
    Jul 2015
    Location
    Cape Town
    Posts
    52
    Thanks
    3
    Thanked 2 Times in 2 Posts

    Exclamation oosterzee box usage

    Please give me some of your input on using an oosterzee box for supplying two different distribution boards on the same premises and of the same building. It is a three phase supply and the Oosterzee box has three separate 50 amp circuit breakers feeding 1 distribution board and a second single phase cable feeding a second smaller distribution board. The second supply is protected by a 45 amp circuit breaker in the oostersee box and is clearly marked as feeding secondary board. The distribution board also has indication that it is fed from the oosterzee box.
    The supply feeding the main distribution board is a 10 mm whilst the second supply is a 6 mm. Although it is a commercial unit the smaller dist board only supplies a kitchen. Both cables are supplied after the council meter. Is there any reason why I should fail this installation?
    To supply the secondary dist board from the main dist board is virtually impossible!
    I cannot see any indication in the code (SANS 10142) to disqualify the installation
    " I'd always rather be on the golf course!! "

  2. #2
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    So you've got a 50A 3-phase main DB and a 45a single phase subDB fed from the oostersee box which in turn is supplied from the meter. What size cable between the meter and the oostersee box? What is the rating of the OCPD at the meter?

    I guess in theory the oostersee box is basically the main DB even though there are no final circuits fed from it. The other 2 boards it supplies are actually sub DB's. If it conforms to all the regs governing a main DB I wouldn't see any reason to disqualify it.
    _______________________________________________

    _______________________________________________

  3. #3
    Full Member markthespark's Avatar
    Join Date
    Jul 2015
    Location
    Cape Town
    Posts
    52
    Thanks
    3
    Thanked 2 Times in 2 Posts
    Thanks Andy I've just never come accross this situation before and although a little concerned, I was more concerned about council regs than sans regs. cable sizing and OCPD rating good to go so I'm happy! just needed extra reassurance!! :-)

  4. #4
    Gold Member Sparks's Avatar
    Join Date
    Dec 2009
    Location
    Port Elizabeth
    Posts
    890
    Thanks
    20
    Thanked 127 Times in 96 Posts
    I agree although I would say a 3ph isolator must be present as "Main Switch" and the existing breakers labelled "Sub DB1" and Sub DB2" and then the sub DBs also labelled accordingly.

  5. #5
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,648
    Thanks
    3,304
    Thanked 2,676 Times in 2,257 Posts
    Blog Entries
    12
    I'm with Sparks - with just one concern remaining -
    Quote Originally Posted by markthespark View Post
    the Oosterzee box has three separate 50 amp circuit breakers feeding 1 distribution board...
    That's the bit that has been worrying me. Is that one breaker per phase?
    If yes, shouldn't this be a 3 phase circuit breaker?

  6. #6
    Gold Member Sparks's Avatar
    Join Date
    Dec 2009
    Location
    Port Elizabeth
    Posts
    890
    Thanks
    20
    Thanked 127 Times in 96 Posts
    Yes I missed that, I thought the boards were supplied with single phase. That specific board would need a 3ph CB after the 3ph isolator.

Similar Threads

  1. [Question] Ethical Usage of the Internet
    By Sandrella Merhej in forum Business Online Forum
    Replies: 23
    Last Post: 23-Jan-13, 12:49 AM
  2. Control bandwidth usage of staff
    By Martinco in forum Technology Forum
    Replies: 23
    Last Post: 01-Dec-10, 11:44 AM
  3. Electrical usage control software
    By Marq in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 21-Sep-09, 03:47 PM
  4. ADSL usage: Are we being ripped off?
    By Marq in forum General Business Forum
    Replies: 9
    Last Post: 29-Jul-08, 02:27 PM
  5. newsletter usage
    By duncan drennan in forum General Business Forum
    Replies: 4
    Last Post: 12-Sep-06, 02:48 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •