Results 1 to 5 of 5

Thread: twin and earth question

  1. #1
    Full Member
    Join Date
    Jun 2016
    Location
    Port Elizabeth
    Posts
    28
    Thanks
    0
    Thanked 1 Time in 1 Post

    twin and earth question

    Hi All. I'm new here an hope to receive some knowledge and learn a lot from all you clever folks.
    My question is : may you use twin an earth to wire complete installation or a part of it but surface mount the twin and earth because reg.6.4.6.1 (b) unarmoured cabels may by used for open wiring(see 6.4.5) and no were the reg.6.4.5.1 does it state that it may be installed within arms reach except 6.4.5.2 were it states "next to beams that can be used for walking on". So one may not install twin and earth surface mount on walls to switches and plugs,why do so many electricians install it that way?

  2. #2
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,924
    Thanks
    576
    Thanked 934 Times in 755 Posts
    Open wiring is defined as
    '6.4.5 Open wiring
    NOTE Open wiring consists of single-core insulated conductors that operate at not
    more than 250 V to earth.'


    It's pretty rare to see open wiring installation nowadays, there used to be 'knob and tube' wiring which had a wrap of bitumen soaked cloth or later vulcanised rubber was used.

    I'm guessing you may be getting confused by the terminology,
    Open wiring is an outdated intentional system of installation where unsheathed wiring (single wires) were used and it run through porcelain tubes whenever it crossed a building structural element and was regularly supported by bobbins along its length.....Not to be confused with exposed wiring which is where wiring or copper conductor is unintentionally accessible often due to some half-wit leaving a lid or cover off something.
    Wire is a single insulated conductor forming only part of a circuit, not to be confused with cable which is multiple insulated conductors (wires) sheathed together. Twin and earth is not wire so doesn't fall under regs governing only wire.
    Insulation is the protection covering a conductor and giving it only electrical protection. Sheathing is the additional layer that gives mechanical and environmental protection to the insulation and the conductor. You get some wire that is sheathed and cables are sheathed. Armour is an additional layer that gives added mechanical and environmental protection. Sometimes the armour layer is further sheathed to protect it from moisture and prevent corrosion.

    6.4.3.4 If a cable is not run on racks or in pipes or ducts, it shall be firmly
    fixed to prevent sagging or creeping.

    This would apply to twin and earth so it can be run surface without containment or rack if it's adequately clipped (or glued, see note 1).
    _______________________________________________

    _______________________________________________

  3. #3
    Full Member
    Join Date
    Jun 2016
    Location
    Port Elizabeth
    Posts
    28
    Thanks
    0
    Thanked 1 Time in 1 Post
    Hi Andy. twin and earth is regarded as unarmoured multi-core thus it is covered by the regs and the reg stipulate that if the is no ceiling it shall be at least 3m above ground level,so if it says 3m above ground level it means it may not be mounted on the surface to switches,plugs and so forth. I could be wrong but that is the way I understand it and that's why I'm trying to find out the real story.

  4. #4
    Full Member
    Join Date
    Oct 2012
    Location
    Durban
    Posts
    66
    Thanks
    0
    Thanked 5 Times in 4 Posts
    As Andy said you are referring to 'open wiring'. Check out 6.3.6 which covers the use of PVC insulated multicore cables. The regs 6.4.6.1 refers to unamoured single core cables.

  5. #5
    Full Member
    Join Date
    Jun 2016
    Location
    Port Elizabeth
    Posts
    28
    Thanks
    0
    Thanked 1 Time in 1 Post
    Hi. Thanx for the reply and I did get confused with the regs and 6.3.6 is the answer I was looking for. Thanks for the answers I rely do appreciate your time guys.

Similar Threads

  1. Coc question Regarding Earth for other services.
    By Jasond MIE in forum Electrical Contracting Industry Forum
    Replies: 38
    Last Post: 13-Dec-19, 07:32 AM
  2. Earth Leakage Unit Question
    By Slow Blow in forum Electrical Contracting Industry Forum
    Replies: 24
    Last Post: 26-Jun-16, 10:50 PM
  3. No earth wire!
    By Dave A in forum Electrical Contracting Industry Forum
    Replies: 27
    Last Post: 02-Jan-16, 08:47 PM
  4. November 2010 Paper 2 Exam Question 1 and Question 2 (ANSWERS)
    By Fikani2010 in forum Electrical Contracting Industry Forum
    Replies: 10
    Last Post: 12-May-13, 10:49 PM
  5. [Opinion] The Twin Towers of South Africa
    By ChrisNG53 in forum South African Politics Forum
    Replies: 3
    Last Post: 07-Dec-10, 12:28 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •