    Odd tripping problem

    One of my CNC machines has developed a rather odd problem. Whenever I turn the machine off it takes the earth leakage protection with it. The machine is in but idle, i.e. the motion controller is holding the stepper motors and the VFD has no output. I suppose the answer would be to disconnect the various systems one at a time and turn the machine on and off a couple of times. It is just such a strange problem...any thoughts.

  2. #2
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    It's most likely the power supplies/noise filters or even the VFD filters. You might be able to narrow it down to one component but it could also be a combination of functional leakage from several things adding up to more than 30mA.

    What else, other than that particular machine, does that earth leakage breaker supply?
    _______________________________________________

    _______________________________________________

  3. #3
    Diamond Member
    Join Date
    Mar 2010
    Location
    Cape Town
    Posts
    6,329
    Thanks
    426
    Thanked 978 Times in 795 Posts
    A whole lot of plugs go through that breaker. The problem only ever occurs when I turn the specific machines off. (Even when there is nothing else connected to the group of plugs. I suppose it could only be the VFD or the power supply to the stepper motors.

Similar Threads

  1. Earth Leakage Breaker (RCD) Tripping
    By AndyD in forum Electrical Contracting Industry Forum
    Replies: 33
    Last Post: 14-Jul-23, 02:53 PM
  2. Nuisance E/L tripping only @ loadshedding
    By joshthejew in forum Electrical Contracting Industry Forum
    Replies: 6
    Last Post: 16-Dec-20, 05:46 AM
  3. Earth leakage tripping when plug in snake rack
    By MattyN in forum Electrical Contracting Industry Forum
    Replies: 7
    Last Post: 22-Aug-15, 09:29 AM
  4. earth leakage tripping
    By ians in forum Electrical Contracting Industry Forum
    Replies: 12
    Last Post: 23-Jun-15, 11:27 AM
  5. Tripping through the minefield.
    By Dave A in forum BEE and Employment Equity Forum
    Replies: 1
    Last Post: 28-Jul-06, 04:21 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •