Please could someone shed some light on how to test a Bundu generator...
I have put my loop tester on the installation to test once the gennie was installed and I am getting some very interestingly illegal readings!
My loop reading is around 7 ohms (way too high), and my PSCC reading is around 48A (way too low)!!
The neutral is earthed and the installation tests perfectly when on mains supply...
I have phoned Bundu on a few occasions and just get given the run around and no one comes back to me.
They say that no one has ever asked them this question before??!
If so, then either, A, every sparky in SA knows exactly how to CoC a Bundu gennie, or B, (my guess) is that no one is CoC'ing them at all!
Well, not the Bundu's anyway...
My client is waiting for his certificate but I cannot issue it as the readings are illegal.
Any help would be greatly appreciated.
Regards
Si


Ps: My mate has the exact same make and model Bundu and I tested his and got almost identical illegal readings...??!