    Sizing of Electrical components

    Hey guys I have got a three phase drill presser here; on the name plate it written, Volt (400.), Ph(3), Pole (4), ,Hz (50),, kW (1.1), r.p.m. (1400), A(2.75), Cos (0.72), type (YS 90), Ins.Cl F, IP (54)& S6-60%. Now my 1st question what size 3 Phase C/B should I use?

  2. #2
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    The circuit breaker is sized according to the circuit, not the appliance. Can you give details of the circuit? Is it on a plug and socket or will it be the only appliance on the circuit and hard wired into a t/pole isolator?
    _______________________________________________

    _______________________________________________

  3. #3
    Junior Member
    Join Date
    Jul 2015
    Location
    Durban
    Posts
    18
    Thanks
    2
    Thanked 0 Times in 0 Posts
    Sorry for the late response Andy, it will be the only appliance connected. It will be 5meters away from the DB that I'll use to power it up. The cable will be run on a cable tray.

  4. #4
    Full Member MullerR's Avatar
    Join Date
    Jan 2016
    Location
    Lady Grey
    Posts
    44
    Thanks
    3
    Thanked 6 Times in 5 Posts
    Does the drill press motor has its own overcurrent relay for in the case of an overcurrent? If so, it can be wired from the db with a 1 or 1.5sqmm surfix,protected by a 5A curve 1 mcb.

  5. #5
    Junior Member
    Join Date
    Jul 2015
    Location
    Durban
    Posts
    18
    Thanks
    2
    Thanked 0 Times in 0 Posts
    Thank you MullerR for your response, if I may ask what formular did you use to size the circurt breaker. If I calculate the current that my drill presser will draw (using P=root3*V*I) I get 1.59Amps.
    from there how do you size your breaker?

  6. #6
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    Your circuit breaker size is calculated from the cable size, the installation method, cable length etc etc. The circuit breaker protects the circuit, not the drill that's connected to it. The drill press motor should be protected by an appropriately sized thermal overload contained within the drill press itself.

    Also you can't calculate the run current of a motor from the kW rating of the motor. The kilowatt rating of a motor is an indication of its mechanical output, not its electrical input. In the good old days we sized motors in Horsepower and a 1 HP (Horsepower) motor meant it could lift the same weight at the same speed as an actual horse which is a measure of its output capabilities. Nowadays we use Kilowatts for the same measure and 1 horsepower is around 0.75kW. This has lead to endless confusion because electrical input is also measured in kilowatts but the electrical input will always be higher than the mechanical output because no motors are 100% efficient and free from losses.

    So basically you can't convert the kilowatt rating of a motor into a run current unless you also know its efficiency, it's power factor and any other losses including friction etc. If you want the run current rather refer to the data on the plate on the side of the motor or the loading graphs supplied by the manufacturer.
    _______________________________________________

    _______________________________________________

  7. #7
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,648
    Thanks
    3,304
    Thanked 2,676 Times in 2,257 Posts
    Blog Entries
    12
    i.e.

    Quote Originally Posted by @SamboLindoh View Post
    Hey guys I have got a three phase drill presser here; on the name plate it written, Volt (400.), Ph(3), Pole (4), ,Hz (50),, kW (1.1), r.p.m. (1400), A(2.75), Cos (0.72),...

  8. #8
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,480
    Thanks
    134
    Thanked 695 Times in 593 Posts
    Blog Entries
    1
    A rule of thumb I use to calculate starting current for a motor is 8:1. So if the motor is a 1Amp motor, the starting current will peak approximately at 8Amps. The period that it remains at 8Amps is directly linked to the load.

    But as Andy says the circuit breaker in the DB is there to protect the wiring, not your load.
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

  9. #9
    Junior Member
    Join Date
    Jul 2015
    Location
    Durban
    Posts
    18
    Thanks
    2
    Thanked 0 Times in 0 Posts
    The drill presser will be the only machinery connected to this circuit breaker there will be no other machinery or appliance connected. the drill presser will be "5m" away from the the DB and the cable will run on a cable rack.Please see the attached name plate for the drill presser.
    Attached Thumbnails Attached Thumbnails Click image for larger version. 

Name:	Drill presser.jpg 
Views:	212 
Size:	19.5 KB 
ID:	6246  

  10. #10
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    Quote Originally Posted by Justloadit View Post
    A rule of thumb I use to calculate starting current for a motor is 8:1. So if the motor is a 1Amp motor, the starting current will peak approximately at 8Amps. The period that it remains at 8Amps is directly linked to the load.

    But as Andy says the circuit breaker in the DB is there to protect the wiring, not your load.
    With small motors the start current would generally only affect the selection of the curve of the circuit breaker. In SA most MCB's are C curve as standard which means they'll tolerate 5-10 times their rated load current without instantaneous tripping which will tolerate most motor start currents. In some EU countries and the UK for example most MCB's are installed as B curve as standard so they would be more likely to nuisance trip with a motor load.

    @Sambo, The fact it's such a small motor limits your circuit design options somewhat so I really wouldn't overthink this too much. Being a drill press it won't be started under any great load so I'd just go with MullerR's suggestion of a 1.5mm Surfix with a 5A C-curve MCB.
    _______________________________________________

    _______________________________________________

Page 1 of 2 12 LastLast

Similar Threads

  1. Sizing Batteries for inverters
    By Tonye in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 24-Feb-16, 11:43 AM
  2. [Question] Preferred make of electrical components
    By MullerR in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 28-Jan-16, 12:42 AM
  3. The fight against sub-standard electrical components
    By Dave A in forum Electrical Contracting Industry Forum
    Replies: 21
    Last Post: 23-Oct-14, 09:07 AM
  4. [Question] where do you get your computer components from?
    By twinscythe12332 in forum Technology Forum
    Replies: 8
    Last Post: 24-Mar-09, 09:46 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •