Thread: Sizing of Electrical components

  1. #11
    Junior Member
    Join Date
    Jul 2015
    Location
    Durban
    Posts
    18
    Thanks
    2
    Thanked 0 Times in 0 Posts

    C/B

    Thank you very much guys, you have given me a fish (Answer) definetly sure I won't go hungry today but however please teach me how to fish now (how did you get about to that 5Amp C-curve MCB ..."METHOD/FORMULAR) THANK YOU ONCE MORE.

  2. #12
    Full Member MullerR's Avatar
    Join Date
    Jan 2016
    Location
    Lady Grey
    Posts
    44
    Thanks
    3
    Thanked 6 Times in 5 Posts
    @sambo. If you read the previous comments from Andy,Dave and Justlaodit, you will see theres no formula here. The drill press has its own overcurrent protection device (supposed to). On the ID plate it states the drill will draw a current of 2.75A. Thus you go and check what wire size can draw those amps on that lenght. Refer to sans 10142-1 for volt drop calculations etc. If you determined the wire size, you must now select the protection device (mcb) to protect the wire (circuit). In this case, if you use a 1.5sqmm Surfix, a 5A mcb is more than sufficient. If you want more info on cables etc, check if you can download the aberdare catalogs. If you cant get hold of them,let me know, i can upload it.

  3. Thank given for this post:

    @SamboLindoh (16-May-16), Dave A (29-Apr-16)

  4. #13
    Junior Member
    Join Date
    Jul 2015
    Location
    Durban
    Posts
    18
    Thanks
    2
    Thanked 0 Times in 0 Posts
    I couldn't please forward it to me MullerR my email is "lindoh.sambo@gmail.com"

    Thank you in advance.

Page 2 of 2 FirstFirst 12

Similar Threads

  1. Sizing Batteries for inverters
    By Tonye in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 24-Feb-16, 11:43 AM
  2. [Question] Preferred make of electrical components
    By MullerR in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 28-Jan-16, 12:42 AM
  3. The fight against sub-standard electrical components
    By Dave A in forum Electrical Contracting Industry Forum
    Replies: 21
    Last Post: 23-Oct-14, 09:07 AM
  4. [Question] where do you get your computer components from?
    By twinscythe12332 in forum Technology Forum
    Replies: 8
    Last Post: 24-Mar-09, 09:46 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •