    CoC Inspection & Test Question

    Under the question "Different circuits are separated electrically", does this only apply to different circuit types (ie. Communications, security, etc) of for different circuits (socket outlets and lights for example) ?

  2. #2
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    I think you might be confusing separation and segregation.
    _______________________________________________

    _______________________________________________

  3. #3
    Full Member
    Join Date
    Jun 2014
    Location
    Somerset West
    Posts
    42
    Thanks
    3
    Thanked 5 Times in 5 Posts
    Quote Originally Posted by AndyD View Post
    I think you might be confusing separation and segregation.
    Probably, but with regards to SECTION 4 on the CoC which are they referring to?

    I assume it refers to the following: Circuits for control communication, security, detection, safety and the like should be electrically separated and, where specified, physically separated.

    So in premises without these other types of circuits does one normally state N/A?

  4. #4
    Bronze Member
    Join Date
    Mar 2012
    Location
    Account_Deleted
    Posts
    165
    Thanks
    122
    Thanked 23 Times in 18 Posts
    IMHO: Eg: Light circuit originates from bottom of breaker, feeds to switch then to and through the load (lightbulb) back to DB through a N.

    If you know feed that same lightbulb let's say from another source, let's say you get a L from another source (breaker) in the same DB (or heavens forbid from another DB - i have seen this) and feed that L through a switch to the same lightbulb in order to switch the light on from 2 different locations. (2-way or intermediate switch to much hassle)

    Now you have a circuit that is not electrically separated. It is not separated from other circuits as it is now joined. You switch off your breaker, even remove the L and proceed to the light fitting to do maintenance.

    Meanwhile the other switch feeding from the other source is closed, thus live and "backfeeding" the circuit and now your circuit, which you removed from the bottom of the breaker and/or the first switch is live. With most lights not on an E/Leakage you suddenly stand with a cocked, loaded gun in your mouth and you think it is a lollipop.

    The circuit was not electrically separated from other electrical circuits.

    Above scenario is on purpose but the conductors can also "burn through" and make other circuits live unexpectedly.

    This is how I was explained to back in 1986.

    PS. the neutral is also part of the circuit. It must be separate too and not part of any other circuit.

    http://electriciancentre.co.uk/how-t...tion-circuits/
    Last edited by ACEsterhuizen; 14-Mar-16 at 12:55 PM. Reason: clarify

  5. Thanks given for this post:

    PaulG (14-Mar-16)

  6. #5
    Full Member
    Join Date
    Jul 2015
    Location
    Cape town
    Posts
    46
    Thanks
    18
    Thanked 5 Times in 5 Posts
    Interesting topic, I'm always finding that guys are connecting eg. All light circuit neutrals together in roofs or sometimes sharing a thicker earth cable between two circuits instead of having two separate thinner earth wires.
    On my opinion each circuit should have its own neutral wire and own earth wire, and the only place these wires from different circuits should be connected together is in the DB on the earth or neutral bars.
    I think it's pretty obvious not to mix lives.
    If you interlink neutrals on a plug circuit inside the home you may end up having to disconnect more than one plug circuit when experiencing earth leakage tripping on a neutral fault before repairing.
    Having circuits separated completely makes fault finding much simpler and in the case of a live to earth fault somewhere, as little equipment as possible will be subjected to this fault voltage.
    That's what I think anyway

  7. #6
    Gold Member Sparks's Avatar
    Join Date
    Dec 2009
    Location
    Port Elizabeth
    Posts
    890
    Thanks
    20
    Thanked 127 Times in 96 Posts
    It is my understanding that each circuit shall have it's own neutral. Not only will that reduce the chance of electric shock, but also aid fault finding. Neutrals are to be connected to a neutral bar so that each circuit can be individually disconnected. This is how I interpret "electrically separated". A light fitting/appliance may have two separate supplies provided it is labelled accordingly.

Similar Threads

  1. Inspection report
    By ians in forum Electrical Contracting Industry Forum
    Replies: 43
    Last Post: 09-Apr-15, 11:07 PM
  2. Labour inspection documents.
    By Musiclover08 in forum Labour Relations and Legislation Forum
    Replies: 3
    Last Post: 30-Jul-14, 11:14 AM
  3. November 2010 Paper 2 Exam Question 1 and Question 2 (ANSWERS)
    By Fikani2010 in forum Electrical Contracting Industry Forum
    Replies: 10
    Last Post: 12-May-13, 10:49 PM
  4. AIA inspection report - how do I reply?
    By Man1 in forum Electrical Contracting Industry Forum
    Replies: 4
    Last Post: 27-Dec-09, 09:24 AM
  5. Inspection by DoL.
    By Dave A in forum General Regulatory Compliance Forum
    Replies: 1
    Last Post: 18-Jan-07, 08:38 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •