    Let get this right ... if I have agate motor and a pool motor fed from the pool DB it marked as a mixed circuit ... in fact I have a very similar situation.

    I have a cable from the main DB to a sub DB on the verandah ... from the sub DB I have a bunch of garden lights ... a pool DB and a gate motor on the same cable ... I have fitted a weather proof isolator at the gate for the gate lights and motor ... a DB at the pool with a light and pool pump ... and day/night switch in the garden feeding lights ... a mixed circuit label on the sub DB on the verandah all I need ?
    Comments are based on opinion...not always facts....that's why people use an alias.

  2. #52
    Gold Member Sparks's Avatar
    Join Date
    Dec 2009
    Location
    Port Elizabeth
    Posts
    890
    Thanks
    20
    Thanked 127 Times in 96 Posts
    The weird and wonderful world SANS in the new SA, unbelieveably even more so than in the old SA. A sub-DB is not a fixed appliance. It is a remote sub-section of the main DB. It therefore stands to reason that each sub-DB must have a dedicated circuit capable of withstanding the total load of said sub-DB. Obviously it must have the correct designation both at the main DB and also at it's location. Fixed appliances on a "mixed" circuit must have isolating devices as must all other fixed appliances, either an isolator or be connected by means of a socket outlet capable carrying the load. A lighting circuit labelled as such may have unswitched lights connected through unswitched socket outlets.

  3. #53
    Gold Member Sparks's Avatar
    Join Date
    Dec 2009
    Location
    Port Elizabeth
    Posts
    890
    Thanks
    20
    Thanked 127 Times in 96 Posts
    If the pool is connected to a plug circuit through an isolator only, yes, that would be a mixed circuit. Should there however be a "pool DB", not according to the COC, there must be a dedicated supply to that sub-DB. Any plugs/lights fed from that sub-DB must also be labelled as such to ensure compliance and safety when working on the installation. Maximum current capacities of thin cables must be adhered to as well.

  4. #54
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    I installed a 16 amp mcb ... the only issue might be the socket on the pool DB which is wired with 2.5 mm wire ... i am sure there is a reg which stats min. 2.5 mm for socket outlets.

    Which I do beleive makes many many old pool DB supplies illegal ... I have seen many old pool DB's wired with 1.5 mm x 2 core armoured cable ... this house I refer to in this post is why we have this issue ... the feed cable to the pool DB is only 1.5 mm.

    The way I understand a mixed circuit ... a garage for example which has plugs and lights on the same circuit both wired with 2.5 mm wire on a single 20 amp circuit breaker would be labelled as a mixed circuit.
    Comments are based on opinion...not always facts....that's why people use an alias.

  5. #55
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,505
    Thanks
    106
    Thanked 146 Times in 139 Posts
    I know of a whole suburb in East London where ALL the houses are wired only with 1,5mm T&E.
    Only the stove circuit is 4mm.

    Geysers the lot on 1,5mm.

    Breakers are 10A lights, 15A plugs and geyser, 30A stove.

    I did not issue a coc for the following reason.
    The wire going to plugs was in conduit inside the wall.
    Now according to Table 6.2(a) 1,5mm has a current carrying capacity of less than 15A if in conduit in the wall.
    Had it been surface mounted , no problem.

    Anyway, someone else provided a coc as is.

    16A socket outlets must be wired with conductors that are rated at not less than 16A. 6.15.3.b.
    1,5mm will be acceptible if surface mounted, but in conduit in the wall the rating drops to below 16A so unacceptable.

    My 2cents worth.

    Derek

  6. #56
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    The 1.5 mm cable is buried directly in the ground ... and not in conduit ... so it would be ok ?
    Comments are based on opinion...not always facts....that's why people use an alias.

  7. #57
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,505
    Thanks
    106
    Thanked 146 Times in 139 Posts
    Quote Originally Posted by ians View Post
    The 1.5 mm cable is buried directly in the ground ... and not in conduit ... so it would be ok ?
    Use table 6.11

    Gets complicated with soil temperature, thermal resistivity, length etc.

    If it's not in conduit, it should be ok with a 15A breaker depending of course on the distance.

    Derek

Page 6 of 6 FirstFirst ... 456

Similar Threads

  1. [Question] Basic Salary
    By mthokomlita in forum Labour Relations and Legislation Forum
    Replies: 2
    Last Post: 27-Jan-15, 11:10 AM
  2. Anyone have some basic Electronics understanding?
    By Dave S in forum General Chat Forum
    Replies: 4
    Last Post: 12-Apr-13, 09:43 AM
  3. What are the Electrical Compliance Certificate Requirements
    By MikeS in forum Electrical Contracting Industry Forum
    Replies: 33
    Last Post: 18-Jun-12, 10:24 PM
  4. [Article] Basic Conditions of Employment Act
    By BBBEE_CompSpec in forum Labour Relations and Legislation Forum
    Replies: 0
    Last Post: 03-Nov-09, 07:05 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •