Thanks for that info AndyD, very informative (even 5 years later). I have a question though, is there a limit on how many milliseconds the RCD should take to trip? I did a check across 37 installed RCD's and the time range from 9 to 203 milliseconds.
Earth Leakage Breaker (RCD) Tripping
Andy - that was an amazing summary that prompted me to sign up and congratulate you.
This is my first ever post.
And also to ask a question which I hope is not deemed too dumb.
How many circuit breakers can one connect on a bank supplied by a single RCB/EL?
Is there a limit or does one break it up for easier management in future fault-finding?
The DBs I have seen mostly have only the plug circuits on EL. Typically 20A C/Bs.
eg - I have seen DBs with 10x20A C/Bs on a single EL. Others with max of 5x20A C/Bs on EL and with 2 or 3 "banks" of these.
Most are "old style" black Samite but some are "new style" DIN rail.
Thx
CComment
Per regulations you can put as many CB after the Earth leakage as you want to - The Earth leakage has to be overloaded protected so in a domestic situation usually 63Amp isolator type earth leakage an it would have a max of 63Amp CB protecting.Andy - that was an amazing summary that prompted me to sign up and congratulate you.
Thx
C
Good practice is to install limited CB after the earth leakage and that is very dependent on usage - Every appliance has a leakage to earth so eventually an earth leakage will trip purely due to the qty of appliances leaking to earth , some worse than others
In smaller house you would do 1 ELU and 3 plug circuits , In a bigger house maybe 2 earth leakages or 3
My previous house I had 5 Earth Leakage units , where I squat now I have 3 and really only need 1 but I don't like struggling when I get home , I prefer drinking a beer in peaceComment