    I have recently heard many conflicting opinions which electrical circuits MUST, MAY and MAY NOT be routed through an Earth Leakage (RCB).

    Can someone please give me a definitive must/may/may not answer for each of the following:

    • Lights (ceiling mounted)
    • Lights (perimeter wall)
    • Normal 3-point plugs (non-dedicated)
    • Geyser
    • Stove
    • Pool Pump
    • UPS
    • Garage door opener
    • Gate motor

    If all of the above is must/may, is it allowable to use a earth leakage with overcurrent protection (RCCB) as a Main Switch?

    Thanks

  2. #2
    Email problem
    Join Date
    Sep 2010
    Location
    cape town
    Posts
    308
    Thanks
    3
    Thanked 43 Times in 37 Posts
    lights : may
    plugs non ded. : must
    geyser : may
    stove : may
    pool pump : must
    ups : may
    garage door opener plug: must
    gate motor: may (if not plugged in)
    you may use an earth leakage with over current as a main switch

  3. Thank given for this post:

    AndyD (09-Nov-15), ursi (09-Nov-15)

  4. #3
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    You may use an earth leakage with overload is a main breaker or you can use a 30mA earth leakage without overload and a separate MCB but it's worth discussing the inconvenience factor with the home owner first. I generally avoid this setup if possible, I install a 100mA earth leakage as a main breaker and use 30mA 2-pole RCBO's for socket circuits which gives discrimination and a lot less headaches. A lot of it also depends on the type of premises and the budget available.
    _______________________________________________

    _______________________________________________

  5. Thanks given for this post:

    ursi (10-Nov-15)

Similar Threads

  1. Geyser not on earth leakage
    By Goobie in forum Electrical Contracting Industry Forum
    Replies: 21
    Last Post: 03-Jan-19, 05:44 PM
  2. [Question] earth leakage required?
    By ians in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 19-Sep-15, 04:46 PM
  3. earth leakage tripping
    By ians in forum Electrical Contracting Industry Forum
    Replies: 12
    Last Post: 23-Jun-15, 11:27 AM
  4. Earth Leakage
    By Pieter00 in forum Electrical Contracting Industry Forum
    Replies: 13
    Last Post: 27-May-13, 12:03 PM
  5. CBI earth leakage units
    By murdock in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 29-Oct-09, 12:44 PM

Tags for this Thread

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •