    earth leakage required?

    I have a really old electrical installation which never had an earth leakage and still doesnt have an earth leakage. The owner has been in the flat for many many many many years and now wants to sell the flat.

    The plugs in the building have been replaced with new plugs many years ago but no extension or addition have been done to the electrical installation. Aircons have been installed directly from the DB using an isolator.

    My advice is to install an earth leakage unit, but the owner feels the electrical installation has worked fine for all these years and now upgrades are required.

  2. #2
    Full Member
    Join Date
    Sep 2015
    Location
    port elizabeth
    Posts
    26
    Thanks
    0
    Thanked 1 Time in 1 Post
    SANS10142-1 section 5.1.3.2 people,animals and property shall be protected against harmful earth fault currents by protective measures such as .. (e) the use of earth leakage protection for socket-outlet circuits.

    Its part of the safety principels so it is a requirement.

    The installation needs to comply for the coc to be issues. The only way ians is to show the customer ther regs and or make him understand that its a requirement.
    Last edited by Dave A; 19-Sep-15 at 11:17 AM.

  3. Thanks given for this post:

    Dave A (19-Sep-15)

  4. #3
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    The customer is moving out the flat, Not his concern any longer. Electrical installation was done way before earth leakage.

  5. #4
    Full Member
    Join Date
    Sep 2015
    Location
    port elizabeth
    Posts
    26
    Thanks
    0
    Thanked 1 Time in 1 Post
    Well if he is selling the flat he needs a coc and for the coc to be issued he needs that installation to comply and to do that he needs the E/L so it is clearly his responsibility or if the new owner agrees he will pay for the E/L being installed and get the installation to comply. But he is still the owner.

Similar Threads

  1. Geyser not on earth leakage
    By Goobie in forum Electrical Contracting Industry Forum
    Replies: 21
    Last Post: 03-Jan-19, 05:44 PM
  2. Does a stove need to be on an earth leakage?
    By Leecatt in forum Electrical Contracting Industry Forum
    Replies: 63
    Last Post: 23-Jan-18, 08:26 AM
  3. [Question] Inverter's and earth leakage
    By padayad28 in forum Electrical Contracting Industry Forum
    Replies: 4
    Last Post: 11-Jul-15, 09:08 AM
  4. earth leakage tripping
    By ians in forum Electrical Contracting Industry Forum
    Replies: 12
    Last Post: 23-Jun-15, 11:27 AM
  5. Earth Leakage
    By Pieter00 in forum Electrical Contracting Industry Forum
    Replies: 13
    Last Post: 27-May-13, 12:03 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •