    Inverter's and earth leakage

    Hi,

    I recently had an inverter installed that supplies a portion of the office during load shedding (lights and computers). Following the installation, we noticed that when plugging appliances into some of the sockets which are not on the inverter circuit causes the inverter earth leakage and the main incomer earth leakage to trip. We replaced the plugs but the problem is still there.

    Any ideas what could be the problem.

  2. #2
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    It sounds like the inverter may be incorrectly connected, it's difficult to say without a lot more info and maybe some photos of the connections etc. Can't you get the installers back to find the problem?
    _______________________________________________

    _______________________________________________

  3. #3
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,648
    Thanks
    3,304
    Thanked 2,676 Times in 2,257 Posts
    Blog Entries
    12
    Quote Originally Posted by AndyD View Post
    Can't you get the installers back to find the problem?
    And did the installers issue you with an electrical Certificate of Compliance for the alteration to the installation?

  4. #4
    Bronze Member
    Join Date
    Mar 2012
    Location
    Account_Deleted
    Posts
    165
    Thanks
    122
    Thanked 23 Times in 18 Posts
    In addition to the above it could also be an unbalanced neutral, which means that one or more plug neutrals (the ones that trips when load is connected) is not connected (Both Live and Neutral) through the Earth Leakage. Time to wire that Inverter and db box correctly :-)
    Attached Thumbnails Attached Thumbnails Click image for larger version. 

Name:	SANS 10142 wire inverter into section of db board.jpg 
Views:	947 
Size:	38.6 KB 
ID:	5707  
    Last edited by ACEsterhuizen; 24-Jun-15 at 10:01 AM. Reason: adding pic

  5. #5
    Platinum Member SilverNodashi's Avatar
    Join Date
    May 2007
    Location
    Johannesburg, South Africa
    Posts
    1,197
    Thanks
    12
    Thanked 188 Times in 136 Posts
    Yup, definitely an unbalanced neutral on some of those sockets.
    Get superfast South African Hosting at WebHostingZone

Similar Threads

  1. Geyser not on earth leakage
    By Goobie in forum Electrical Contracting Industry Forum
    Replies: 21
    Last Post: 03-Jan-19, 05:44 PM
  2. Does a stove need to be on an earth leakage?
    By Leecatt in forum Electrical Contracting Industry Forum
    Replies: 63
    Last Post: 23-Jan-18, 08:26 AM
  3. earth leakage tripping
    By ians in forum Electrical Contracting Industry Forum
    Replies: 12
    Last Post: 23-Jun-15, 11:27 AM
  4. Earth Leakage
    By Pieter00 in forum Electrical Contracting Industry Forum
    Replies: 13
    Last Post: 27-May-13, 12:03 PM
  5. CBI earth leakage units
    By murdock in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 29-Oct-09, 12:44 PM

Tags for this Thread

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •