  1. #31
    Bronze Member
    Join Date
    Oct 2014
    Location
    Pretoria
    Posts
    126
    Thanks
    16
    Thanked 16 Times in 15 Posts
    Whaaat!?!! R25k and here I was thinking that P&T technologies asking R10k was ridiculous, ai

  2. #32
    Junior Member
    Join Date
    Sep 2014
    Location
    Cape Town
    Posts
    15
    Thanks
    0
    Thanked 4 Times in 3 Posts
    P@T was the cheapest I could find, was worth it there, they were pretty jacked up.

  3. #33
    Bronze Member
    Join Date
    Oct 2014
    Location
    Pretoria
    Posts
    126
    Thanks
    16
    Thanked 16 Times in 15 Posts
    Quote Originally Posted by Jasond MIE View Post
    P@T was the cheapest I could find, was worth it there, they were pretty jacked up.
    Thnx for the heads up. I heard someone closer to me is cheaper, but looking at P&T they look professional.
    I am guessing you did the masters under option 1 - 3? not 4?

  4. #34
    Silver Member
    Join Date
    Jul 2008
    Location
    Germiston, South Africa
    Posts
    397
    Thanks
    24
    Thanked 47 Times in 43 Posts
    The installation of this earthing Terminal has been a requirement for some time now in new installations.
    I have never seen one.
    I have just read an article that specifically states that it is a requirement for an earthing Terminal to be fitted into existing installations, Sparks Magazine - April 2015 - Page 18. "The earthing terminal for other services - a piece in the jigsaw.
    Herwith the link: http://crown.co.za/images/magazines/...April_2015.pdf

    My question is "What does this item look like and where does one put it in a domestic installation?

    I cant imagine an Earth Terminal bolted onto the DB Facia plate and having 5 copper wires dangling from it would compliment the decor of the lounge in a mid-floor townhouse unit.

    Who has installed one of these and how do you go about it.
    I believe it has to be bonded to the consumers earth terminal via a 6mm copper wire?

  5. #35
    New Member
    Join Date
    Feb 2016
    Location
    Fish Hoek
    Posts
    6
    Thanks
    6
    Thanked 0 Times in 0 Posts

    SANS 10142-1 2017 update

    In SANS-10142-1 (2017), Section 6.11.5 now reads " A readily accessible earthing terminal may be provided...

    So it looks like this has become optional then. Am I right?

    There is still lots about putting up labels to indicate where it is and to mark it.

    Thanks.

  6. #36
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,648
    Thanks
    3,304
    Thanked 2,676 Times in 2,257 Posts
    Blog Entries
    12
    Quote Originally Posted by JacksonS View Post
    In SANS-10142-1 (2017), Section 6.11.5 now reads " A readily accessible earthing terminal may be provided...

    So it looks like this has become optional then. Am I right?
    Correct.

  7. #37
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,484
    Thanks
    104
    Thanked 141 Times in 134 Posts
    Quote Originally Posted by Dave A View Post
    Correct.
    Not 100% correct.

    On some installations this earthing terminal for other services is optional because of the words " may be installed"


    However:


    See Regulation 6.13.2.6. Other services such as water,gas,etc. in conductive material, which enter the premises, SHALL be bonded to the readily accessible earthing
    terminal ( see 6.11.5 ) by means of a conductor of cross sectional area at least 2,5mm sq copper or equivalent.



    From the above regulation it is clear that when the water or gas supply to the installation is in metal piping then the earthing terminal for other services is not optional. It is a requirement.

    Cheers and peace out

    Derek

  8. Thanks given for this post:

    Dave A (12-Dec-19)

  9. #38
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,648
    Thanks
    3,304
    Thanked 2,676 Times in 2,257 Posts
    Blog Entries
    12
    Great point, Derlyn.

    Shades of the satellite dish discussion...

  10. #39
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    So why not mount the non conductive dish on a non conductive pole and save all the hassle and reduce the risk of "attracting" lighting... and all the hassle of the rules and regs with regards to earthing? This is what i am doing with the wireless bridges we are installing... mount them on non conductive poles and wow imagine that less risk of lightning... but we all knew that.
    Comments are based on opinion...not always facts....that's why people use an alias.

Page 4 of 4 FirstFirst ... 234

Similar Threads

  1. Earth Leakage Unit Question
    By Slow Blow in forum Electrical Contracting Industry Forum
    Replies: 24
    Last Post: 26-Jun-16, 10:50 PM
  2. Earth Leakage
    By Pieter00 in forum Electrical Contracting Industry Forum
    Replies: 13
    Last Post: 27-May-13, 12:03 PM
  3. November 2010 Paper 2 Exam Question 1 and Question 2 (ANSWERS)
    By Fikani2010 in forum Electrical Contracting Industry Forum
    Replies: 10
    Last Post: 12-May-13, 10:49 PM
  4. Possible SEO services scam from Omega Services - be careful
    By SilverNodashi in forum Scam Alert Forum
    Replies: 3
    Last Post: 29-Jan-11, 11:43 AM
  5. Google Earth
    By Faan in forum General Business Forum
    Replies: 0
    Last Post: 30-Jul-08, 08:52 PM