Quote Originally Posted by DieterT View Post
I always compare the electrical regulations with the bible. When doing study of the bible you never just pull something out of context and make that your thing to live by. You reference it with different parts of the bible, read all that is before and after that specific piece and if you really want to make sure you know your stuff even look at different translations.
Apart from the different translations, the SANS 10142-1 for electrical installations (non - hazardous/medical locations or specialized earthing) is treated in most cases the same as doing bible study.
I gently suggest it is this type of analogy approach that has got the industry into such a regulatory tangle in the first place. It really is much simpler, and certainly way more appropriate, to consistently apply the principles of law to the understanding of law (and regulations) in my opinion. It is bound to produce a far better quality product that requires less divine intervention to decipher and understand.

Let me try to restore your faith in the principles of law a little.

In my own quest for clarity, I have now gone hunting for references to section 6.11 in section 5, and found 5.1.3.1 which reads

A new electrical installation shall not be connected to the supply unless the supply includes a protective conductor. (See also 6.11 and 8.7.3.)
This plainly applies to a new electrical installation only, otherwise why include the word "new". If it had been the intent that it applies to all electrical installations (and all supplies for that matter), it should have read -

"An electrical installation shall not be connected to a supply unless the supply includes a protective conductor. (See also 6.11 and 8.7.3.)"

So in the instance where we are dealing with an existing installation, we are effectively directed to look elsewhere. If this was not the intent, those with input into these codes need to ensure the words match their intent.